I think that the horse has been beaten to death here.
But will the OP tell all the solutions when this issue has been resolved ? |
![]() |
![]() |
![]() |
#102 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#103 |
Senior Member
|
![]()
For $10.99 at Lowe's, suggest you get a roll of 3M high temperature flue tape, high heat sealing tape up to 600 degrees, 15-foot roll x 1.5", silver color and add some more tape to the metal exhaust pipe behind the boiler, especially where it makes a 90-degree turn as shown in your photo. A very small and smelly amount of exhaust could be getting out, there, where the exhaust vent pipe hook-up takes a sharp turn between the boiler and the brick chimney.
https://www.truevalue.com/15-ft-hi-t...lver-flue-tape .... a fix for leaky chimney pipe connections where one section fits into the next with a friction fit. To test for an exhaust leak, simply hold your hand up to the joint connection. Google this: "Even Low Levels of Soot Can Be Deadly to Older People, Research Finds" ..... January 26, 2022: NY Times ..... especially the reader's comments down the bottom
__________________
... down and out, liv'n that Walmart side of the lake! Last edited by fatlazyless; 01-26-2022 at 09:47 AM. |
![]() |
![]() |
![]() |
#104 |
Senior Member
Join Date: Jan 2003
Location: Alton Bay
Posts: 5,596
Blog Entries: 2
Thanks: 2,453
Thanked 1,979 Times in 1,080 Posts
|
![]()
Replace the pipe.
The high temp tape is good on joints on the chimney, but in my humble opinion, shouldn't be hard to patch a pipe. Think Flex Seal. Good to stop a leak on the boat bottom while out on the water, but certainly not a permanent solution. Dave
__________________
I Live Here... I am always UPTHESAUKEE !!!! |
![]() |
![]() |
![]() |
#105 | |
Senior Member
|
![]() Quote:
![]()
__________________
... down and out, liv'n that Walmart side of the lake! |
|
![]() |
![]() |
Sponsored Links |
|
![]() |
#106 |
Senior Member
Join Date: Jun 2020
Location: Alton Bay
Posts: 68
Thanks: 24
Thanked 23 Times in 17 Posts
|
![]()
Nope ...... its still moving! Lets beat this topic a bit more!
|
![]() |
![]() |
![]() |
#107 |
Senior Member
|
![]()
Well ....... so far all posts have discussed adjusting or improving the combustion or burning the fuel oil to eliminate the smell with no mention on tightening up the exhaust.
Wrapping that silver, high-heat, duct tape around each joint is an easy do-it-yourself fix that works excellent to seal it up. Taking a fast look at the Beckett burner ... http://www.beckettcorp.com/product-c...ntial-burners/... ![]()
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
![]() |
#108 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
To my knowledge, the AFUE is not the perfect measure of whether the burn is clean. It is a measure of Fuel Used vs Heat Produced. Units with chimneys generally need to ''give up'' some heat into the flue to achieve draft.
High efficiency models tend to use direct vent, or power vent, to limit the amount of heat that needs to be lost up the chimney. |
![]() |
![]() |
![]() |
#109 |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]()
What do the readers' comments say? They're not accessible to people who evade the fire wall. (Not that I would do that.)
|
![]() |
![]() |
![]() |
#110 |
Senior Member
|
![]()
There are 239 different comments so far that vary in length, and all comments need to be rational and real to be shown and they come from the U.S., Canada, Mexico and around the world. A 7-day/week, NY Times internet subscription costs $1/week for the first year, and $17/month, after the first year. While the article is mostly medical science, the readers' email comments are mostly personal experience and opinion.
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
![]() |
#111 | |
Member
Join Date: Jan 2005
Posts: 45
Thanks: 142
Thanked 14 Times in 11 Posts
|
![]() Quote:
He seems to know his stuff too |
|
![]() |
![]() |
![]() |
#112 |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]()
I've received the bills for the two service calls, totaling $440. Here's what was done, according to the bills:
First call:
|
![]() |
![]() |
![]() |
#113 |
Senior Member
|
![]()
That exhaust is made with different steel stove pipe sections that fit together like a Lego and it usually will have some small leaks at the joints that can be tightened up using small sheet metal screws and/or high heat duct tape.
To check it for leaks around the seams, use a little dishwashing soap and water in a spritzer bottle and spray it on the vent pipe exhaust. Any soap bubbles forming and growing indicate a leak when the oil pump/electrode/nozzle/fan blower powers up the boiler. Each stove pipe joint should go good with three small sheet metal screws and high heat duct tape to seal it up.
__________________
... down and out, liv'n that Walmart side of the lake! Last edited by fatlazyless; 02-01-2022 at 06:40 AM. |
![]() |
![]() |
![]() |
#114 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
Soap bubbles??? The chimney should have a negative draft not positive draft! If you don't you have a problem. |
|
![]() |
![]() |
The Following User Says Thank You to swnoel For This Useful Post: | ||
root1 (02-14-2022) |
![]() |
#115 | |
Senior Member
|
![]() Quote:
Hit it with more hi-heat duct tape and clean the outside so's the tape will stick, good.
__________________
... down and out, liv'n that Walmart side of the lake! |
|
![]() |
![]() |
The Following User Says Thank You to fatlazyless For This Useful Post: | ||
SailinAway (02-01-2022) |
![]() |
#116 |
Senior Member
Join Date: Apr 2004
Location: Central NJ
Posts: 82
Thanks: 74
Thanked 25 Times in 16 Posts
|
![]()
Our previous (first house) had an oil fired steam boiler. The previous owner had a service contract with Company A. The first morning in the house we had no heat, called the company and they came out. They had already serviced the boiler that year before the start of the season. I don’t know how many times we had to call them that winter due to problems with the boiler. We might have kept them a second year, but it was a long time ago. I just don’t remember. We changed to Company B for service and oil. They would come at the beginning of the season, clean and service everything. When we moved out 14 years later, we still had the same boiler and never had to call for it having a problem. Oh, and it also provided the domestic hot water for the house, so it ran year round.
The difference was in the service company. |
![]() |
![]() |
![]() |
#117 | |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() Quote:
Just curious how long you were in the HVAC field? What blower fan are you talking about and what obstruction? I did this for years and am willing to learn from someone apparently with more expertise that I. |
|
![]() |
![]() |
![]() |
#118 |
Senior Member
|
![]()
The blower fan is an integral part of the gun that includes the motor, electrode, nozzle, oil pump, and fan.
The obstruction is that 90-degree vent pipe attached to the back of the boiler which force exhaust against the vent seam on the side. Vent pipe sections do not always make a tight fit and need three small sheet metal screws and hi-heat duct tape to seal it up. ...... ![]() ![]() I graduated from Fast Eddy's 12-Week School of Oil Burner Technology where the emphasis was all about doing it FAST ...... and ABLE to convince the customer that you know what the heck you are doing down in their basement with thaht olde oil burner because you got it done, FAST, and talked all about the fuel oil combustion/filthy dirty OIL soot build-up/electrode/nozzle/oil pump/fan blower, all synchronized together in perfect combustion harmony as you was hitting the oil burner with a FAST tune-up. .... ![]() Steve Lavimoniere the oil burner man: North Dartmouth, Massachusetts; Sept 17, 2020 ..... www.youtube.com/watch?v=1T1s9JSHol4 ..... Smell ... ![]() So, why do people go with natural gas by pipe or liquid propane in the tank when it costs more and has less btu's than residential fuel oil? Because it burns cleaner and usually needs way less service calls including no yearly boiler/furnace clean-out/tune-up.
__________________
... down and out, liv'n that Walmart side of the lake! Last edited by fatlazyless; 02-05-2022 at 08:19 AM. |
![]() |
![]() |
![]() |
#119 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
On a boiler?
If I am next to my boiler, I can hear the draft down the flue... but I don't think that it is forced. |
![]() |
![]() |
![]() |
#120 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]() Quote:
But you probably hear that after it gets going. I think there can be a bit of positive pressure at start. When Chimney and everything is cold. The furnace needs to ignite quick and burn as clean and complete as it can until a draft gets going as quick as possible. During that period it does not run good. The longer it's trying to push air up the chimney the more chance you'll get that initial smell. It could be so many things that can cause a poor/slow ignite or a slow draft. Electrodes worn Electrodes not adjusted Electrodes not clean Electrodes insulator cracked or dirty Cold Fuel Chimney Damaged (water and ice in the chimney) Nozzle wrong Nozzle clogged Oil pump not adjusted to the correct pressure Oil pump worn Wrong air intake Obstruction in chamber And probably a dozen more. Note I didn't list pin holes in that flue pipe because those are rarely air tight nor do they need to be. In fact it might be doing you a favor if some smell is coming through that connector pipe because it's telling you, you have a bigger problem. If you make that air tight you might be just be masking a bigger problem. Just call them again or find someone else is all you can do. I would also get a chimney guy out since the Chimney is so old. |
|
![]() |
![]() |
The Following User Says Thank You to mswlogo For This Useful Post: | ||
fatlazyless (02-05-2022) |
![]() |
#121 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
I thought my flue damper was to prevent blow back when wind forces the draft to reverse.
|
![]() |
![]() |
![]() |
#122 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
The draft regulators purpose is to maintain the correct over fire draft. Some boilers do not require them. They do nothing for downdrafts. My guess is you're hearing the upward draft. Many times you'll see and or hear the regulator bouncing. This should also be checked and adjusted at the time of an annual service.
|
![]() |
![]() |
![]() |
#123 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
I don't hear the damper.
Only when near the flue, I hear the boiler kick on... then a little while later I hear the draft of exhaust running through the flue. |
![]() |
![]() |
![]() |
#124 |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]()
I've stopped the smoke odor in the house by blocking the gap under the door from the cellar to the upstairs. When the furnace is running I can smell the odor inside/around the smoke pipe, about 8 to 10 inches above the bend. Does this tell you anything?
|
![]() |
![]() |
![]() |
#125 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]() Quote:
A good clean install shouldn’t have to be air tight there. Because a good chimney should have a draft. For an old chimney you can cut it some slack (takes a bit for a draft to get going). How much slack is acceptable, I don’t know. If it’s a constant leak, I think it’s a fairly serious issue (not the hole itself but the fact it wants to come out the hole). Like I said, regardless of your issues, like the furnace itself you need to maintain your chimney too. Oil furnaces are especially hard on them because gases are acidic. So get your chimney checked. Chimney guy can probably fix the vent pipe too. |
|
![]() |
![]() |
![]() |
#126 | |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#127 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]()
Without knowing what the stack temp is it's hard to know if it's possibly after drip. Is the boiler partially plugged? I know you had 2 pros come out ... sorry to say it's time to have someone else.
|
![]() |
![]() |
![]() |
#128 |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]() |
![]() |
![]() |
![]() |
#129 |
Senior Member
Join Date: Jan 2006
Posts: 6,700
Thanks: 751
Thanked 1,454 Times in 1,011 Posts
|
![]()
Who would believe we have 128 posts about furnace filters???
![]() ![]() |
![]() |
![]() |
The Following User Says Thank You to tis For This Useful Post: | ||
Seaplane Pilot (02-09-2022) |
![]() |
#130 |
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
![]() |
![]() |
![]() |
![]() |
#132 |
Senior Member
Join Date: May 2008
Posts: 102
Thanks: 2
Thanked 6 Times in 6 Posts
|
![]() |
![]() |
![]() |
![]() |
#133 |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]()
Motion to not to end it.
I’d like to learn how this gets resolved. Is there now a shortage on characters? If you are not interested, don’t read it. No, it wasn’t his filter. He’s tried hard to get it resolved and it’s not resolved yet. I think SailinAway needs to try another Pro though. I’d recommend a Chimney Pro next though. He may need another Oil guy too. |
![]() |
![]() |
![]() |
#134 |
Senior Member
|
![]()
You all need to know the title for this thread "Changing furnace filter" contains a basic misunderstanding because it is definitely a boiler shown in the original poster's photographs and not a furnace, and that a boiler is VERY different from a furnace! .....
![]() A boiler will heat up WATER for heat, while a furnace will heat up AIR for heat, making it a "hot water boiler" or a "hot air furnace" ...... you understand! .. ![]() For a very good chimney inspection/cleaning/repair/expertise, suggest you try the Chimney Crickett from Exit 29 in Thornton, Rick Vollmer, who has been doing chimneys for a long time! He goes all over central NH in his big white Chimney Crickett van with the ladders on the roof.
__________________
... down and out, liv'n that Walmart side of the lake! |
![]() |
![]() |
The Following User Says Thank You to fatlazyless For This Useful Post: | ||
mswlogo (02-11-2022) |
![]() |
#135 | |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#136 | |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]() Quote:
I bet 95% of people would say "furnace" in this sentence: It's cold in here; let's turn on the _______. |
|
![]() |
![]() |
The Following User Says Thank You to SailinAway For This Useful Post: | ||
mswlogo (02-11-2022) |
![]() |
#137 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#138 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
I use the term ''boiler''.
|
![]() |
![]() |
![]() |
#139 |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
![]() |
![]() |
![]() |
The Following 3 Users Say Thank You to mswlogo For This Useful Post: | ||
![]() |
#140 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
It is what the industry calls them.
|
![]() |
![]() |
![]() |
#141 |
Senior Member
Join Date: Apr 2004
Posts: 104
Thanks: 0
Thanked 9 Times in 8 Posts
|
![]()
We had a rental with forced hot air heat by oil l. The tenants would occasionally complain of an odor. I had the furnace serviced every year and each time I mentioned the odor. The technician tested carbon monoxide and efficiency. Both good. I had co detectors in the living space per code so I wasn't too concerned.
I had the old furnace replaced a couple of years ago and the technician discovered that the heat exchanger had 3 inch hole that rusted through. It was probably there for years and no one checked for it. So if you smell something when the furnace is running check the heat exchanger. Last edited by loony; 02-13-2022 at 11:26 PM. |
![]() |
![]() |
![]() |
#142 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
If there was a hole in a boiler heat exchanger wouldn't the burner flood with water?
|
![]() |
![]() |
![]() |
#143 |
Senior Member
Join Date: Dec 2016
Posts: 2,048
Thanks: 210
Thanked 652 Times in 435 Posts
|
![]()
Had a crack in my boiler about 10!years ago. Didn’t flood, just felt like a bath house minis the grape leaf’s
Sent from my iPhone using Winnipesaukee Forum mobile app |
![]() |
![]() |
![]() |
#144 |
Senior Member
Join Date: Apr 2004
Posts: 104
Thanks: 0
Thanked 9 Times in 8 Posts
|
![]() |
![]() |
![]() |
![]() |
#145 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
The system being discussed with the problem is a boiler.
|
![]() |
![]() |
![]() |
#146 |
Senior Member
Join Date: Jul 2010
Location: Laconia, Lake Opechee
Posts: 187
Thanks: 286
Thanked 90 Times in 48 Posts
|
![]()
Can we close this thread? Enough!
|
![]() |
![]() |
![]() |
#147 |
Senior Member
Join Date: Jun 2021
Posts: 3,354
Thanks: 3
Thanked 592 Times in 488 Posts
|
![]()
We have yet to hear the what the solution to the issue is.
|
![]() |
![]() |
The Following User Says Thank You to John Mercier For This Useful Post: | ||
SailinAway (02-16-2022) |
![]() |
#148 |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]() |
![]() |
![]() |
The Following 2 Users Say Thank You to SailinAway For This Useful Post: | ||
mswlogo (02-17-2022), Newbiesaukee (02-17-2022) |
![]() |
#149 |
Senior Member
Join Date: Apr 2019
Posts: 991
Thanks: 256
Thanked 280 Times in 169 Posts
|
![]()
So, the oil company canceled the second bill and wanted to replace the smoke pipe for $300, which I think they should have done in the first place. I sort of lost my faith in that company and I think I'll look for someone else to do the work.
|
![]() |
![]() |
The Following User Says Thank You to SailinAway For This Useful Post: | ||
Descant (03-30-2022) |
![]() |