Hard to say without being there, but the most of the loads you described should have been within the capability of a 5.5 kW Honda. The killer for overloading generators in most cases is any high surge startup loads such as a well pump and HVAC blowers and compressors. In many cases even these are possible to power if you add a soft start device to your high surge loads. By equipping your air handlers with soft start mechanisms you might be able to run those as well and keep your home equally conditioned during an outage.
|
![]() |
![]() |
The Following User Says Thank You to NH.Solar For This Useful Post: | ||
sunset on the dock (03-10-2025) |
![]() |
#2 |
Senior Member
Join Date: Apr 2004
Location: formerly Winter Harbor, still Wolfeboro
Posts: 1,190
Thanks: 301
Thanked 527 Times in 294 Posts
|
![]()
In early 2000 I wanted to install a generator. The electrician suggested a unit large enough to carry the entire house, auto-transfer, weekly auto-exercise, and an over-sized LP tank. My reaction was "over-sell", and we talked about it for a while, and I finally agreed to his plan. The was the best decision. Never had a problem. When we moved, I wanted a generator, called (now a different electrician) the electrician, told him I wanted a unit large enough to carry the whole house, auto-transfer, weekly auto-exercise, and extra LP tanks. He was silent for a moment, then said, "You've done this before." Yes, so that is what I had installed. It isn't cheap, but it is money well-spent, peace of mind, and one less "system" to worry about. The punch line by me about generators is very simple" "Go big, go auto-auto, and have periodic (annual) service".
|
![]() |
![]() |
The Following User Says Thank You to camp guy For This Useful Post: | ||
sunset on the dock (03-10-2025) |
![]() |
#3 |
Senior Member
Join Date: Apr 2004
Location: Lakes Region
Posts: 695
Thanks: 22
Thanked 99 Times in 68 Posts
|
![]()
When some outlets work, and some don't, you may have dropped a leg and only have half your panel powered. Your 220v appliances (air handler?) will not work and any of those 220V devices that remain connected, such as baseboard heat, will energize the dead leg through high resistance and cause a low voltage/brownout condition on that side of the panel. That can cause all kinds of weird effects on circuits on that side, such as dim bulbs and motors that won't run - like perhaps your fish filters? Check your connections at the generator, on the transfer switch, any cords you may use, and inside your panel...
|
![]() |
![]() |