Hard to say without being there, but the most of the loads you described should have been within the capability of a 5.5 kW Honda. The killer for overloading generators in most cases is any high surge startup loads such as a well pump and HVAC blowers and compressors. In many cases even these are possible to power if you add a soft start device to your high surge loads. By equipping your air handlers with soft start mechanisms you might be able to run those as well and keep your home equally conditioned during an outage.
__________________
Peter
NH Solar
NH.Solar is offline   Reply With Quote
The Following User Says Thank You to NH.Solar For This Useful Post:
sunset on the dock (03-10-2025)
Old 03-09-2025, 02:59 PM   #2
camp guy
Senior Member
 
camp guy's Avatar
 
Join Date: Apr 2004
Location: formerly Winter Harbor, still Wolfeboro
Posts: 1,190
Thanks: 301
Thanked 527 Times in 294 Posts
Default Generator installation

In early 2000 I wanted to install a generator. The electrician suggested a unit large enough to carry the entire house, auto-transfer, weekly auto-exercise, and an over-sized LP tank. My reaction was "over-sell", and we talked about it for a while, and I finally agreed to his plan. The was the best decision. Never had a problem. When we moved, I wanted a generator, called (now a different electrician) the electrician, told him I wanted a unit large enough to carry the whole house, auto-transfer, weekly auto-exercise, and extra LP tanks. He was silent for a moment, then said, "You've done this before." Yes, so that is what I had installed. It isn't cheap, but it is money well-spent, peace of mind, and one less "system" to worry about. The punch line by me about generators is very simple" "Go big, go auto-auto, and have periodic (annual) service".
camp guy is offline   Reply With Quote
The Following User Says Thank You to camp guy For This Useful Post:
sunset on the dock (03-10-2025)
Old 03-09-2025, 03:14 PM   #3
TomC
Senior Member
 
TomC's Avatar
 
Join Date: Apr 2004
Location: Lakes Region
Posts: 695
Thanks: 22
Thanked 99 Times in 68 Posts
Default

When some outlets work, and some don't, you may have dropped a leg and only have half your panel powered. Your 220v appliances (air handler?) will not work and any of those 220V devices that remain connected, such as baseboard heat, will energize the dead leg through high resistance and cause a low voltage/brownout condition on that side of the panel. That can cause all kinds of weird effects on circuits on that side, such as dim bulbs and motors that won't run - like perhaps your fish filters? Check your connections at the generator, on the transfer switch, any cords you may use, and inside your panel...
TomC is online now   Reply With Quote
The Following User Says Thank You to TomC For This Useful Post:
sunset on the dock (03-10-2025)
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 01:12 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.

This page was generated in 0.11637 seconds