Referring back to my earlier post (#14) on this thread, to give you an idea of the impact of making the house in the "superinsulated" class, consider what we have. The gross conditioned space is about 4,000 sqft (two levels on a 2K footprint). The heating system is a 2-ton geo unit, and even when it dips below zero (like last week when it was -8F one morning), the thing is keeping the house at 70 F in just first stage, putting out about 75% of capacity.

Back in 2011, the area distributor for Climatemaster and two of their "approved installers" all proposed putting in a 5-ton unit, even though I gave them the spreadsheet showing that a 2-ton unit would suffice. I doubt they had any experience in sizing a unit for a house like this one, so they just used canned software and assumptions as to what the house was like, many of which were wrong. The only set of operating data I have that seems useful is for a period of several days when the temperature swung just a few degrees either side of zero. Apparently my calculations were a bit conservative by over 10%, which I am told is typical for such a house.

In the case of geo heat (or minisplits), the cost of the unit does depend strongly on its capacity, so proper sizing based on a really good heat loss calculation, not shortcuts, is essential. For a fired heat source, the unit installed typically is grossly oversized, even for a house built just "to code."

Last edited by DickR; 02-01-2022 at 06:34 PM. Reason: word choice
DickR is offline   Reply With Quote
Old 02-01-2022, 08:25 PM   #2
mswlogo
Senior Member
 
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
Default

Quote:
Originally Posted by DickR View Post
Referring back to my earlier post (#14) on this thread, to give you an idea of the impact of making the house in the "superinsulated" class, consider what we have. The gross conditioned space is about 4,000 sqft (two levels on a 2K footprint). The heating system is a 2-ton geo unit, and even when it dips below zero (like last week when it was -8F one morning), the thing is keeping the house at 70 F in just first stage, putting out about 75% of capacity.

Back in 2011, the area distributor for Climatemaster and two of their "approved installers" all proposed putting in a 5-ton unit, even though I gave them the spreadsheet showing that a 2-ton unit would suffice. I doubt they had any experience in sizing a unit for a house like this one, so they just used canned software and assumptions as to what the house was like, many of which were wrong. The only set of operating data I have that seems useful is for a period of several days when the temperature swung just a few degrees either side of zero. Apparently my calculations were a bit conservative by over 10%, which I am told is typical for such a house.

In the case of geo heat (or minisplits), the cost of the unit does depend strongly on its capacity, so proper sizing based on a really good heat loss calculation, not shortcuts, is essential. For a fired heat source, the unit installed typically is grossly oversized, even for a house built just "to code."
Just got my first Geothermal estimate. $47K !!!

4 Ton for 2300 sq ft well insulated (2x6 construction dense foam).

My guess is a 2 or 3 ton would work and let the backup kick in when needed.
mswlogo is offline   Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 08:54 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.

This page was generated in 0.17052 seconds