The good news is that the generator works wonderfully! The bad news is that it is SO loud!! We find it difficult to sleep in the house when it is running and we feel badly about what our neighbors must be hearing.
Any suggestions? We are thinking about building something around the generator with access doors and vents. Thanks! |
![]() |
![]() |
![]() |
#2 |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 6,231
Thanks: 2,382
Thanked 5,276 Times in 2,050 Posts
|
![]()
There is one thing you can do that will make a big difference and that is to extend your exhaust and pipe it into a 5 gallon or larger bucket of water. It will make all the difference in the world and won't hurt the performance of the generator.
DO NOT attempt to build a cover for your generator. Most likely your generator is air cooled and needs all the air it can get to stay cool. Any attempt at all to cover it, even if you add vents will not allow it to cool properly and you will burn it up. Dan |
![]() |
![]() |
The Following User Says Thank You to ishoot308 For This Useful Post: | ||
welchislandman (11-07-2011) |
![]() |
#3 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]()
Extending the exhaust as already suggested, may help. I've done it with mine but I'm not sure yet if it's done more than move the carbon monoxide further from the house. I've heard of the water bucket trick but keep in mind that will add back-pressure to your unit which may, or may not, make a difference in performance. Variations on this include running the exhaust into a 'dry-well' filled with gravel or adding another small muffler at the end of the run.
I also put a piece of plywood about a foot from the genny as a noise-screen. I think this helps deflect a bit of the noise. It might be more effective if I added a piece of foam to the back of it. Good luck! |
![]() |
![]() |
![]() |
#4 |
Senior Member
Join Date: Dec 2010
Location: Winnisquam, NH
Posts: 613
Thanks: 419
Thanked 163 Times in 115 Posts
|
![]()
We did the plywood trick all the time at different job sites. It was more of a defection I think, because it was just as loud on the other side. Might not work with the neighbors.
__________________
"I'd rather be ridin than rolling" |
![]() |
![]() |
![]() |
#5 |
Senior Member
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
|
![]()
Replace that cheap little muffler that it came with.
|
![]() |
![]() |
The Following User Says Thank You to AB_Monterey For This Useful Post: | ||
Rattlesnake Guy (11-07-2011) |
Sponsored Links |
|
![]() |
#6 |
Senior Member
Join Date: Mar 2009
Location: Welch Is, Gilford
Posts: 79
Thanks: 91
Thanked 8 Times in 8 Posts
|
![]()
With our 6000w gen I noticed my govenor was set to full throttle. with my load, I was able reduce the setback and ensured the voltage was not lower than 230v on the meter. Lowered the noise quite a bit since it wasnt running wide open. I also dont run my gen at night and restart it early am to get the heat/water back running.
|
![]() |
![]() |
![]() |
#7 |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
![]() EEKS, looks to me as if that maybe running in a closed or partially closed area.
__________________
|
![]() |
![]() |
![]() |
#8 |
Senior Member
Join Date: Jun 2009
Location: Soon to be Moultonboro
Posts: 258
Thanks: 1
Thanked 81 Times in 34 Posts
|
![]()
Diesel work every time.
![]() ![]()
__________________
"Government is not reason, it is not eloquence, it is force; like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action.....Unknown....but attributed to George Washington |
![]() |
![]() |
![]() |
#9 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
![]()
With the temps we had in this outage there was no need to run the gen all night long.Get up a little early,start it up and the house is warm in an hour.
__________________
SIKSUKR |
![]() |
![]() |
![]() |
#10 |
Member
Join Date: Jan 2005
Posts: 20
Thanks: 0
Thanked 0 Times in 0 Posts
|
![]()
Shouldn't change the governor setting. The motor has to run at multiples of 60 to maintain 60HZ power frequency. Small portable generators typically will run at 3600 rpm to maintain the 60hz power frequency.
|
![]() |
![]() |
![]() |
#11 | |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
![]() Quote:
![]()
__________________
|
|
![]() |
![]() |
![]() |
#12 |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,944
Thanks: 544
Thanked 570 Times in 335 Posts
|
![]()
Some of those are inverter generators. They basically make a lower-voltage that is run through a circuit to great 120V/60Hz power. So, the motor speed does not directly effect the power cycle frequency of the power generated.
__________________
[insert witty phrase here] |
![]() |
![]() |
![]() |
#13 |
Senior Member
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 951
Thanks: 252
Thanked 351 Times in 158 Posts
|
![]()
Wow...that is really taking a chance...hope you have a CO detector or two.
BT
__________________
" Live for today because yesterday is gone and tomorrow may never come" |
![]() |
![]() |
![]() |
#14 |
Senior Member
Join Date: Apr 2004
Posts: 2,591
Thanks: 150
Thanked 229 Times in 166 Posts
|
![]()
Another way to go a little quiter is spending good money and purchasing a Honda or equivalent. These units are tolerable but will set you back a few thousand dollars.
|
![]() |
![]() |
![]() |
#15 |
Senior Member
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
|
![]()
Boys,
It wasn't running in that location. ![]() |
![]() |
![]() |
![]() |
#16 |
Senior Member
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 410 Times in 251 Posts
|
![]()
Lots of folks run them in a garage with the windows open to vent the fumes and reduce the noise.
|
![]() |
![]() |
![]() |
#17 | |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
![]() Quote:
![]()
__________________
|
|
![]() |
![]() |
![]() |
#18 | |
Senior Member
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 951
Thanks: 252
Thanked 351 Times in 158 Posts
|
![]() Quote:
BT
__________________
" Live for today because yesterday is gone and tomorrow may never come" |
|
![]() |
![]() |
![]() |
#19 |
Senior Member
Join Date: Apr 2004
Posts: 57
Thanks: 4
Thanked 7 Times in 4 Posts
|
![]() |
![]() |
![]() |
![]() |
#20 |
Senior Member
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
|
![]()
That's a detached shed btw.
But with that car muffler on there (got it at the dump), that thing is QUIET. |
![]() |
![]() |
![]() |
#21 |
Junior Member
Join Date: Jun 2010
Posts: 11
Thanks: 4
Thanked 0 Times in 0 Posts
|
![]()
Interesting discussion and certainly safety trumps noise in our priorities!
To clarify our generator situation, it is full house disconnect located in the yard outside our house. We live in the house year round but part-time. In our research we found a company (Acoustiblok out of Florida - primarily industrial applications) that sells sound absorbing panels. They sent us a picture of a solid fence with their panels on the inside surrounding the four sides of a residential generator. Something we are considering. Thanks for the suggestions, of all kinds! |
![]() |
![]() |
![]() |
#22 |
Senior Member
Join Date: Apr 2004
Location: Kuna ID
Posts: 2,755
Thanks: 246
Thanked 1,942 Times in 802 Posts
|
![]() |
![]() |
![]() |
![]() |
#23 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
![]()
I would have to assume that BR was talking about a detached garage and or shed. Never run one in an attached garage or garage under even with the doors open. If its really stormy out I have enough wire to reach my detached shed(75 ft) away. I just face the exhaust out the door and don't spend any time in there during or after for a few days.
__________________
SIKSUKR |
![]() |
![]() |
![]() |
#24 |
Senior Member
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 410 Times in 251 Posts
|
![]()
I honestly did believe anyone would think otherwise, but I guess I was wrong.
I know of several people who have their transfer switch located inside their garage or run them inside the garage with extension cords going into the house. This allows the security of having the generator inside instead of outside where it can be stolen as many have been. |
![]() |
![]() |
![]() |
#25 | |
Senior Member
Join Date: Mar 2010
Posts: 392
Thanks: 177
Thanked 146 Times in 76 Posts
|
![]() Quote:
I know of several propane fired standby generators that are in enclosed buildings, these generators have been there for Years without any issues. Unfortunately the most important key ingredient, Common Sense is severely lacking in todays society |
|
![]() |
![]() |
The Following User Says Thank You to MarkinNH For This Useful Post: | ||
Belmont Resident (11-09-2011) |
![]() |
#26 | |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,944
Thanks: 544
Thanked 570 Times in 335 Posts
|
![]() Quote:
A gas/diesel genset in an enclosed space operated by a homeowner is a recipe for death, especially if that enclosed space has any ability to exchange air with a living space.
__________________
[insert witty phrase here] |
|
![]() |
![]() |
![]() |
#27 |
Senior Member
Join Date: Mar 2010
Posts: 392
Thanks: 177
Thanked 146 Times in 76 Posts
|
![]() |
![]() |
![]() |
![]() |
#28 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,302
Thanks: 67
Thanked 171 Times in 127 Posts
|
![]()
I always thought those things ran on butane. I'm pretty sure propane does produce carbon-monoxide. There are catalytic heaters that use propane that can be used indoors but motors can be hazardous.
|
![]() |
![]() |
![]() |
#29 |
Senior Member
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 951
Thanks: 252
Thanked 351 Times in 158 Posts
|
![]()
Common sense is not that common any more.....
__________________
" Live for today because yesterday is gone and tomorrow may never come" |
![]() |
![]() |
![]() |
#30 |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
![]()
I think we are
![]() ![]()
__________________
|
![]() |
![]() |
![]() |
#31 |
Senior Member
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 410 Times in 251 Posts
|
![]()
You could always hook up an exhaust hose and vent it outside of the detatched holding area. Thats what they do in all automobile repair shops.
I do like the idea of the extended muffler because I'll bet the end never even gets warm so you could use just about any hose to vent the exhaust. |
![]() |
![]() |