Default Furnace leak ?

Went to down to cellar and noticed a small puddle around furnace. Enough water to wipe-up with a sponge, maybe a 1/2 -3/4 cup water. Doesn't seem to be coming from any pipes but under furnace ?
Just had serviced 2 months ago and all was good.

Furnace has never leaked before but it is 19 yrs old the fuse has been set!
Typical Beckette/Burnham setup. Contractor grade when house was built 19 yrs ago.

Thoughts??? Hoping this is not serious, but if the boiler is cracked, could be a replacement and with Christmas a month away not the greatest time, at least this didn't happen in the middle of Jan or Feb.

Just as a side note, I'm in process of selling house this Spring, and pushed this out from last summer. Note to self, never hesitate a decision, it may come around to bite you !
bigdog is offline   Reply With Quote
Old 11-27-2016, 05:22 PM   #2
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

Quote:
Originally Posted by bigdog View Post
Went to down to cellar and noticed a small puddle around furnace. Enough water to wipe-up with a sponge, maybe a 1/2 -3/4 cup water. Doesn't seem to be coming from any pipes but under furnace ?
Just had serviced 2 months ago and all was good.

Furnace has never leaked before but it is 19 yrs old the fuse has been set!
Typical Beckette/Burnham setup. Contractor grade when house was built 19 yrs ago.

Thoughts??? Hoping this is not serious, but if the boiler is cracked, could be a replacement and with Christmas a month away not the greatest time, at least this didn't happen in the middle of Jan or Feb.

Just as a side note, I'm in process of selling house this Spring, and pushed this out from last summer. Note to self, never hesitate a decision, it may come around to bite you !
Sounds like a boiler, is the water coming from the pressure valve, usually there is an open ended pipe attached to these valves. If that is the case, then the fix is relatively cheap. On the other hand, Burnham is notorious for cracked castings. I had two one covered by warranty the second I cut my losses and bought a different boiler. Even the warranty was expensive as they don't pay labor. Sorry for your problems.

Last edited by ITD; 12-03-2016 at 09:41 PM. Reason: put correct valve type in.
ITD is offline   Reply With Quote
Old 11-27-2016, 06:33 PM   #3
TheProfessor
Senior Member
 
Join Date: Nov 2010
Posts: 1,062
Thanks: 17
Thanked 325 Times in 198 Posts
Default

Sounds like a boiler and not a furnace.

If it continues then time for a service call.
TheProfessor is offline   Reply With Quote
Old 11-27-2016, 06:37 PM   #4
Barney Bear
Senior Member
 
Join Date: May 2004
Posts: 962
Thanks: 495
Thanked 273 Times in 174 Posts
Default Water Leak

Had our home hot air furnace serviced this fall. After the service call, a leak was discovered. The service man came back to secure a hose connection that was loosened during the previous visit. No charge, of course, for the return visit.
Barney Bear is offline   Reply With Quote
Old 11-28-2016, 05:25 AM   #5
swnoel
Senior Member
 
Join Date: Jan 2007
Posts: 527
Thanks: 83
Thanked 194 Times in 118 Posts
Default

Quote:
Originally Posted by ITD View Post
Sounds like a boiler, is the water coming from the T+P valve, usually there is an open ended pipe attached to these valves. If that is the case, then the fix is relatively cheap. On the other hand, Burnham is notorious for cracked castings. I had two one covered by warranty the second I cut my losses and bought a different boiler. Even the warranty was expensive as they don't pay labor. Sorry for your problems.




http://f.tqn.com/y/homerepair/1/W/F/5/-/-/T_P_Valve.jpg
Really... that's a relief valve for a domestic water tank NOT a boiler! There IS a difference!
swnoel is offline   Reply With Quote
Sponsored Links
Old 11-28-2016, 08:31 AM   #6
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

Quote:
Originally Posted by swnoel View Post
Really... that's a relief valve for a domestic water tank NOT a boiler! There IS a difference!
Your right, I messed it up. It's a pressure relief valve, I was confusing the btu rating of the boiler valve with T and P valve, which would have too high a pressure value for most boilers. Sorry.

Last edited by ITD; 12-03-2016 at 09:39 PM.
ITD is offline   Reply With Quote
Old 11-28-2016, 03:01 PM   #7
Biggd
Senior Member
 
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,748
Thanks: 1,961
Thanked 1,070 Times in 675 Posts
Default

I had the same issue with my boiler of similar age. Spent $800 on repairs and had other problems soon after. I threw away $800, should have just replaced it to begin with. My new boiler is so much more efficient also. And since it's a second home the peace of mind of not having problems is priceless. Boilers will last more than 20 years but they aren't nearly as efficient as the newer units.
Biggd is offline   Reply With Quote
Old 11-28-2016, 06:58 PM   #8
nhcatrider
Senior Member
 
Join Date: Mar 2014
Posts: 167
Thanks: 19
Thanked 29 Times in 27 Posts
Default

I just replaced a boiler in a house I bought last summer. The boiler was so old it had a Shell Oil service sticker on it. Had the chimney cleaned at the same time and a huge amount of carbon and soot was removed. The installer figured the previous owner had been running diesel in it all winter last year. The new furnace will pay for itself in about 5 years, less if oil spikes high again. If it's leaking, replace it. It's not worth the hassle of multiple repairs.
nhcatrider is offline   Reply With Quote
Old 11-28-2016, 09:07 PM   #9
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,410
Thanks: 307
Thanked 117 Times in 94 Posts
Default Furnace leak ?

Furnace leak was a false alarm.... Whew... Dodged that bullet.
Thought at first, I had a cracked boiler liner.

Sort of jumped to a conclusion, without first diagnosing the underlying issue.

Where you see water leaking, it's not necessarily that source.
The water was leaking from gasket on a Circulating valve, dropping down on the motor, running underneath, the onto the floor. Hence, I thought was coming from the boiler itself, not so !

Had HVAC service tech replace two 'football shaped' gaskets, on valve flanges,
and that did the trick.

However, after reviewing the entire system it was determined the expansion tank above furnace had no air. This was causing my pipes to gurgle and bubble sounds I've been hearing. Must have had a leak in expansion bladder ?

Also had to replace a release valve about expansion tank, and also a faucet valve on back of boiler.

Hour and half of labor, plus parts under $200

Case closed for the time being......
bigdog is offline   Reply With Quote
Old 11-28-2016, 09:27 PM   #10
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

Quote:
Originally Posted by bigdog View Post
Furnace leak was a false alarm.... Whew... Dodged that bullet.
Thought at first, I had a cracked boiler liner.

Sort of jumped to a conclusion, without first diagnosing the underlying issue.

Where you see water leaking, it's not necessarily that source.
The water was leaking from gasket on a Circulating valve, dropping down on the motor, running underneath, the onto the floor. Hence, I thought was coming from the boiler itself, not so !

Had HVAC service tech replace two 'football shaped' gaskets, on valve flanges,
and that did the trick.

However, after reviewing the entire system it was determined the expansion tank above furnace had no air. This was causing my pipes to gurgle and bubble sounds I've been hearing. Must have had a leak in expansion bladder ?

Also had to replace a release valve about expansion tank, and also a faucet valve on back of boiler.

Hour and half of labor, plus parts under $200

Case closed for the time being......
That's good news, the bladders in those tanks do go, money well spent.
ITD is offline   Reply With Quote
Old 11-29-2016, 10:52 AM   #11
Biggd
Senior Member
 
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,748
Thanks: 1,961
Thanked 1,070 Times in 675 Posts
Default

Quote:
Originally Posted by bigdog View Post
Furnace leak was a false alarm.... Whew... Dodged that bullet.
Thought at first, I had a cracked boiler liner.

Sort of jumped to a conclusion, without first diagnosing the underlying issue.

Where you see water leaking, it's not necessarily that source.
The water was leaking from gasket on a Circulating valve, dropping down on the motor, running underneath, the onto the floor. Hence, I thought was coming from the boiler itself, not so !

Had HVAC service tech replace two 'football shaped' gaskets, on valve flanges,
and that did the trick.

However, after reviewing the entire system it was determined the expansion tank above furnace had no air. This was causing my pipes to gurgle and bubble sounds I've been hearing. Must have had a leak in expansion bladder ?

Also had to replace a release valve about expansion tank, and also a faucet valve on back of boiler.

Hour and half of labor, plus parts under $200

Case closed for the time being......
That's a fair price. Who did you use?
Biggd is offline   Reply With Quote
Old 11-29-2016, 03:17 PM   #12
noreast
Senior Member
 
Join Date: Mar 2015
Posts: 648
Thanks: 316
Thanked 120 Times in 93 Posts
Default

Quote:
Originally Posted by bigdog View Post
Furnace leak was a false alarm.... Whew... Dodged that bullet.
Thought at first, I had a cracked boiler liner.

Sort of jumped to a conclusion, without first diagnosing the underlying issue.

Where you see water leaking, it's not necessarily that source.
The water was leaking from gasket on a Circulating valve, dropping down on the motor, running underneath, the onto the floor. Hence, I thought was coming from the boiler itself, not so !

Had HVAC service tech replace two 'football shaped' gaskets, on valve flanges,
and that did the trick.

However, after reviewing the entire system it was determined the expansion tank above furnace had no air. This was causing my pipes to gurgle and bubble sounds I've been hearing. Must have had a leak in expansion bladder ?

Also had to replace a release valve about expansion tank, and also a faucet valve on back of boiler.

Hour and half of labor, plus parts under $200

Case closed for the time being......
That's usually the problem. Good for you!
noreast is offline   Reply With Quote
Old 11-30-2016, 01:01 PM   #13
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,410
Thanks: 307
Thanked 117 Times in 94 Posts
Default

Biggd,

Work was performed at my other house in Mass. !

Bigdog
bigdog is offline   Reply With Quote
Old 11-30-2016, 02:53 PM   #14
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

FWIW, I had a relief valve that kept purging on my Becket boiler. I assumed the automatic water feed was bad because I could watch the pressure on the boiler go past the normal 12-15 lbs. I replaced and had the same issue. I have a tankless coil in the boiler and it turned out that the coil had a hole and the pressure from my domestic water supply (50 lbs) was leaking into the boiler water and raising it. Lesson learned. BTW..easily replaced by myself.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 12-03-2016, 08:39 PM   #15
swnoel
Senior Member
 
Join Date: Jan 2007
Posts: 527
Thanks: 83
Thanked 194 Times in 118 Posts
Default

Quote:
Originally Posted by ITD View Post
It's a T and P valve, no difference except maybe the size and shape by manufacturer or application, it's still a t and p valve, really. Here's a hint, hot water heater heats water, a boiler.......... heats water. The T and P valve prevents over pressurization from runaway heat or other malfunction.
That is NOT for a boiler... again that is for a domestic hot water tank!!! Please do not offer information that is wrong! I've been doing this for decades and this kind of misinformation can cause damage and bodily harm!
swnoel is offline   Reply With Quote
Old 12-03-2016, 09:40 PM   #16
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

Quote:
Originally Posted by swnoel View Post
That is NOT for a boiler... again that is for a domestic hot water tank!!! Please do not offer information that is wrong! I've been doing this for decades and this kind of misinformation can cause damage and bodily harm!
You're right, I messed it up and doubled down, fixed it now.
ITD is offline   Reply With Quote
The Following User Says Thank You to ITD For This Useful Post:
swnoel (12-04-2016)
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 04:55 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.24155 seconds