Old 10-18-2018, 01:53 PM   #1
TheProfessor
Senior Member
 
Join Date: Nov 2010
Posts: 1,062
Thanks: 17
Thanked 325 Times in 198 Posts
Default Propane Furnace - Service and/or Repair

Seeking an independent propane gas heat contractor.
For possible repair and annual maintenance.

Any names, addresses, phone numbers.
TheProfessor is offline   Reply With Quote
Old 10-19-2018, 03:34 PM   #2
Kamper
Senior Member
 
Kamper's Avatar
 
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,295
Thanks: 67
Thanked 165 Times in 125 Posts
Default

Not much help but... Many plumbers handle gas appliances also. My plumber is almost a neighbor, or I'd give you his number.

Good luck!
Kamper is offline   Reply With Quote
Old 10-19-2018, 10:15 PM   #3
lakevet
Member
 
Join Date: Apr 2017
Posts: 27
Thanks: 2
Thanked 1 Time in 1 Post
Default

Steve Buy heating and cooling in Moultonborough. I pass his building all the time. Just spoke to him this week to service my propane system. I haven't used him but he sounded like a good guy.

Sent from my SAMSUNG-SM-G920A using Winnipesaukee Forum mobile app
lakevet is offline   Reply With Quote
Old 10-21-2018, 09:54 AM   #4
rozbeezer
Member
 
Join Date: Mar 2009
Posts: 24
Thanks: 1
Thanked 4 Times in 4 Posts
Default Central NH H&C

Call Noel Gagnon at Central NH Heating and Cooling.
603-290-3429
He did a great job of changing out my old propane forced air unit for a new one this past spring.
Steve Buy was recommended to me, but he said he couldn't look at my job for 3 months--not a great reply since we were without heat.
rozbeezer is offline   Reply With Quote
Old 10-22-2018, 08:28 AM   #5
Not to Worry
Senior Member
 
Join Date: Dec 2013
Posts: 191
Thanks: 93
Thanked 84 Times in 55 Posts
Default Steve Buy

Called him several times. Always took call but never would set up a time to do work. Thought he was a real find but not so much now.
Not to Worry is offline   Reply With Quote
Sponsored Links
Old 10-23-2018, 06:59 AM   #6
BroadHopper
Senior Member
 
BroadHopper's Avatar
 
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,504
Thanks: 3,113
Thanked 1,089 Times in 783 Posts
Default Gas appliances

In the past Don Morin has faithfully maintained and install my appliances.
He is retired. However Jarrod who use to work for him has continued the business. Give him a call at 603.293.5600
__________________
Someday may never be an actual day.
BroadHopper is offline   Reply With Quote
Old 10-23-2018, 07:15 AM   #7
Biggd
Senior Member
 
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,733
Thanks: 1,952
Thanked 1,068 Times in 673 Posts
Default

Quote:
Originally Posted by Not to Worry View Post
Called him several times. Always took call but never would set up a time to do work. Thought he was a real find but not so much now.
It seems like all contractors are extremely busy now and short on help.
I have a few close friends that run service companies that can't even find general laborers.
The good ones tend to take care of their regular customers and don't have the time or the help to take on new ones.
It's just a sign of the times. A lot of the American youth today go to college and don't want jobs that require getting their hands dirty.
Biggd is online now   Reply With Quote
Old 10-23-2018, 08:16 AM   #8
Not to Worry
Senior Member
 
Join Date: Dec 2013
Posts: 191
Thanks: 93
Thanked 84 Times in 55 Posts
Default Agreed but.....

Quote:
Originally Posted by Biggd View Post
It seems like all contractors are extremely busy now and short on help.
I have a few close friends that run service companies that can't even find general laborers.
The good ones tend to take care of their regular customers and don't have the time or the help to take on new ones.
It's just a sign of the times. A lot of the American youth today go to college and don't want jobs that require getting their hands dirty.
I was a customer. He was great!! Then when I was simply looking for a regular service call he could not arrange a time. I understand if he is busy...just say that versus putting the customer off over and over again. IMHO some of these contractors do not get that service is the gravy train that allows them to make money in both good and bad times.

Not to worry I found someone else to do the annual service.
Not to Worry is offline   Reply With Quote
Old 10-23-2018, 09:24 AM   #9
Biggd
Senior Member
 
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,733
Thanks: 1,952
Thanked 1,068 Times in 673 Posts
Default

Quote:
Originally Posted by Not to Worry View Post
I was a customer. He was great!! Then when I was simply looking for a regular service call he could not arrange a time. I understand if he is busy...just say that versus putting the customer off over and over again. IMHO some of these contractors do not get that service is the gravy train that allows them to make money in both good and bad times.

Not to worry I found someone else to do the annual service.
I had the same issue with my fence guy. He had been repairing my fence for the past 20 years.
He came and looked at it back in May, said he would take care of it, and never returned after repeated calls.
I have a new fence guy now and he did a terrific job. He wasn't very complimentary of the guy who did the repairs in the past. He said they were done half a$$ed.
Biggd is online now   Reply With Quote
Old 10-23-2018, 11:54 AM   #10
tis
Senior Member
 
tis's Avatar
 
Join Date: Jan 2006
Posts: 6,386
Thanks: 716
Thanked 1,375 Times in 951 Posts
Default

It is true, they are all extremely busy now, but I agree, just tell people that. Answer the phone or return the call and say you are too busy.
tis is online now   Reply With Quote
Old 10-23-2018, 02:49 PM   #11
MeredithMan
Senior Member
 
MeredithMan's Avatar
 
Join Date: Aug 2013
Location: Bedford, NH; Meredith, NH
Posts: 862
Thanks: 233
Thanked 768 Times in 302 Posts
Default Lakes Region HVAC

We've been very pleased with Lakes Region HVAC. We have Geothermal Heat & AC, as well as a propane-fired, wall-mounted boiler. LRHVAC has taken good care of all our gear, both for pro-active cleaning/maintenance, as well as any repairs. 603-286-2290
MeredithMan is offline   Reply With Quote
Old 11-08-2018, 02:08 PM   #12
Light Breeze
Member
 
Join Date: Apr 2018
Location: Long Bay and Franklin, Ma
Posts: 23
Thanks: 0
Thanked 2 Times in 2 Posts
Default

Same here LRHVAC has been very good to deal with for us....
Light Breeze is offline   Reply With Quote
Old 01-12-2019, 11:05 AM   #13
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default LaFlamme Plumbing ?

Has any Forum member used LaFlamme Plumbing & Heating in Laconia for gas furnace maintenance ?
bigdog is offline   Reply With Quote
Old 01-15-2019, 11:22 AM   #14
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Propane Service Review

My Propane furnace seems to be constantly running and not sure why ?
Stats: Trans 90 XL (90k BTU output)

Gas service tech checked furnace and nothing appears to be wrong, all 3 gas jets firing OK.

The thing is the zone thermostat (Honeywell( indicates the tempperature is set at 67 degrees, however, the room temperature reading indicates 65 degrees.
Consequently the furnace never shuts down because it is constantly calling for heat to reach the thermostat setting.

New batteries were installed in 'all' house thermostats.

Do you think I have a bad thermostat ?

Thanks,
BD
bigdog is offline   Reply With Quote
Old 01-15-2019, 02:08 PM   #15
Kamper
Senior Member
 
Kamper's Avatar
 
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,295
Thanks: 67
Thanked 165 Times in 125 Posts
Default

BD....

Maybe. Do they have access to the rooms air flow? If they are blocked, they may never reach the right temperature. Most thermostats are easy to change but multi-zones might need a tech to get them to function in harmony.
Kamper is offline   Reply With Quote
Old 01-15-2019, 02:22 PM   #16
fatlazyless
Senior Member
 
fatlazyless's Avatar
 
Join Date: Apr 2004
Posts: 8,506
Blog Entries: 1
Thanks: 291
Thanked 950 Times in 692 Posts
Default ...... propane-911

If all else fails, call the propane expert, call www.christianrepair.com for a propane-911 service call .... what you should have done in the first place.


Plumbing & cHeating; what happens when you call the plumber to fix a heating problem. You get cHeated. What you want is a heating technician. The plumbers don't call it 'Plumbing and cHeating' for nothing.
__________________
... down and out, liv'n that Walmart side of the lake!

Last edited by fatlazyless; 01-15-2019 at 03:05 PM.
fatlazyless is offline   Reply With Quote
Old 01-15-2019, 03:12 PM   #17
Phantom
Senior Member
 
Phantom's Avatar
 
Join Date: Jul 2005
Location: Berlin, Ma / Gilford
Posts: 1,931
Thanks: 445
Thanked 604 Times in 340 Posts
Default

Thanks for the recommendation FLL ….. been looking for someone to run a routine maintenance check on our Rinnai direct vent propane heaters. As they are a Rinnai dealer - they may be just the ticket I have been looking for. Foley., whom we used in the past- dropped this service.
__________________
A bad day on the Big Lake (although I've never had one) - Still beats a day at the office!!
Phantom is offline   Reply With Quote
Old 01-15-2019, 03:26 PM   #18
swnoel
Senior Member
 
Join Date: Jan 2007
Posts: 527
Thanks: 83
Thanked 194 Times in 118 Posts
Default

Quote:
Originally Posted by bigdog View Post
My Propane furnace seems to be constantly running and not sure why ?
Stats: Trans 90 XL (90k BTU output)

Gas service tech checked furnace and nothing appears to be wrong, all 3 gas jets firing OK.

The thing is the zone thermostat (Honeywell( indicates the tempperature is set at 67 degrees, however, the room temperature reading indicates 65 degrees.
Consequently the furnace never shuts down because it is constantly calling for heat to reach the thermostat setting.

New batteries were installed in 'all' house thermostats.

Do you think I have a bad thermostat ?

Thanks,
BD

This is common when a furnace is under fired. It might say 90K btu's on the tag, but if the gas line is too small it will only allow whatever the line size does. Have you ever had problems in cold weather before? Could be the thermostat, is it a programmable? Is this a zoned system... check the dampre and make sure it's opened all the way.
swnoel is offline   Reply With Quote
Old 01-15-2019, 03:44 PM   #19
WinnisquamZ
Senior Member
 
WinnisquamZ's Avatar
 
Join Date: Dec 2016
Posts: 1,865
Thanks: 192
Thanked 589 Times in 394 Posts
Default

Honeywell is one of the worst reviewed thermostats on the market. I would replace it before you dig to deep


Sent from my iPhone using Winnipesaukee Forum mobile app
WinnisquamZ is offline   Reply With Quote
Old 01-15-2019, 03:58 PM   #20
joey2665
Senior Member
 
joey2665's Avatar
 
Join Date: Sep 2008
Location: Meredith Bay & LI, NY
Posts: 3,220
Thanks: 1,204
Thanked 1,007 Times in 648 Posts
Default

Quote:
Originally Posted by WinnisquamZ View Post
Honeywell is one of the worst reviewed thermostats on the market. I would replace it before you dig to deep


Sent from my iPhone using Winnipesaukee Forum mobile app
I agree. I replaced all my Honeywells with Nest and they are excellent
joey2665 is offline   Reply With Quote
Old 01-21-2019, 07:05 AM   #21
Hawley
Junior Member
 
Join Date: Aug 2012
Posts: 14
Thanks: 0
Thanked 2 Times in 2 Posts
Default Hawley

TAKE THE THERMOSTAT OFF THE WALL. iF THE UNIT STOPS THEN THE PROBLEM IS THE THERMOSTAT. iF IT CONTINUES TO RUN. mAY BE A SHORT IN THE WIRE OR , GAS VALVE OR RELAY.
Hawley is offline   Reply With Quote
Old 01-21-2019, 09:58 AM   #22
BroadHopper
Senior Member
 
BroadHopper's Avatar
 
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,504
Thanks: 3,113
Thanked 1,089 Times in 783 Posts
Default Furnace size

Not sure how big your unit is, but Riannai suggest 150k unit for my 1100 sq ft condo with 2 full baths. It includes on demand hot water and 2 zones baseboard heat. It is a condensing boiler so the thermostat is set to go off and on at .1 degree +-. It appears to be running constantly but runs efficiently at that setting. A 30% fuel savings after replacing a conventional boiler. Savings calculation include compensation for temperature variance.

When the boiler is in 'away' mode. The temperature is set to 40". Also the baseboard circulator is constantly running to avoid freezing the pipes. Maybe that is what you are experiencing?

Quote:
Originally Posted by bigdog View Post
My Propane furnace seems to be constantly running and not sure why ?
Stats: Trans 90 XL (90k BTU output)

Gas service tech checked furnace and nothing appears to be wrong, all 3 gas jets firing OK.

The thing is the zone thermostat (Honeywell( indicates the tempperature is set at 67 degrees, however, the room temperature reading indicates 65 degrees.
Consequently the furnace never shuts down because it is constantly calling for heat to reach the thermostat setting.

New batteries were installed in 'all' house thermostats.

Do you think I have a bad thermostat ?

Thanks,
BD
__________________
Someday may never be an actual day.
BroadHopper is offline   Reply With Quote
Old 01-21-2019, 08:31 PM   #23
songkrai
Senior Member
 
Join Date: Dec 2009
Posts: 723
Thanks: 35
Thanked 145 Times in 98 Posts
Default

Quote:
Originally Posted by fatlazyless View Post
If all else fails, call the propane expert, call www.christianrepair.com for a propane-911 service call .... what you should have done in the first place.
Nope. Response from this guy was slow. Then nothing.
songkrai is offline   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 07:58 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.24521 seconds