The good news is that the generator works wonderfully! The bad news is that it is SO loud!! We find it difficult to sleep in the house when it is running and we feel badly about what our neighbors must be hearing.

Any suggestions? We are thinking about building something around the generator with access doors and vents. Thanks!
pkadventures is offline   Reply With Quote
Old 11-06-2011, 08:57 AM   #2
ishoot308
Senior Member
 
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,930
Thanks: 2,289
Thanked 4,940 Times in 1,916 Posts
Default

There is one thing you can do that will make a big difference and that is to extend your exhaust and pipe it into a 5 gallon or larger bucket of water. It will make all the difference in the world and won't hurt the performance of the generator.

DO NOT attempt to build a cover for your generator. Most likely your generator is air cooled and needs all the air it can get to stay cool. Any attempt at all to cover it, even if you add vents will not allow it to cool properly and you will burn it up.

Dan
ishoot308 is offline   Reply With Quote
The Following User Says Thank You to ishoot308 For This Useful Post:
welchislandman (11-07-2011)
Old 11-06-2011, 09:08 AM   #3
Kamper
Senior Member
 
Kamper's Avatar
 
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,296
Thanks: 67
Thanked 166 Times in 126 Posts
Default

Extending the exhaust as already suggested, may help. I've done it with mine but I'm not sure yet if it's done more than move the carbon monoxide further from the house. I've heard of the water bucket trick but keep in mind that will add back-pressure to your unit which may, or may not, make a difference in performance. Variations on this include running the exhaust into a 'dry-well' filled with gravel or adding another small muffler at the end of the run.

I also put a piece of plywood about a foot from the genny as a noise-screen. I think this helps deflect a bit of the noise. It might be more effective if I added a piece of foam to the back of it.

Good luck!
Kamper is offline   Reply With Quote
Old 11-06-2011, 08:08 PM   #4
Winnisquamguy
Senior Member
 
Winnisquamguy's Avatar
 
Join Date: Dec 2010
Location: Winnisquam, NH
Posts: 613
Thanks: 419
Thanked 163 Times in 115 Posts
Default

Quote:
Originally Posted by Kamper View Post
I also put a piece of plywood about a foot from the genny as a noise-screen. I think this helps deflect a bit of the noise. It might be more effective if I added a piece of foam to the back of it.

Good luck!
We did the plywood trick all the time at different job sites. It was more of a defection I think, because it was just as loud on the other side. Might not work with the neighbors.
__________________
"I'd rather be ridin than rolling"
Winnisquamguy is offline   Reply With Quote
Old 11-06-2011, 09:26 PM   #5
AB_Monterey
Senior Member
 
AB_Monterey's Avatar
 
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
Default

Replace that cheap little muffler that it came with.
Attached Images
 
AB_Monterey is offline   Reply With Quote
The Following User Says Thank You to AB_Monterey For This Useful Post:
Rattlesnake Guy (11-07-2011)
Sponsored Links
Old 11-07-2011, 09:42 AM   #6
welchislandman
Senior Member
 
welchislandman's Avatar
 
Join Date: Mar 2009
Location: Welch Is, Gilford
Posts: 79
Thanks: 91
Thanked 8 Times in 8 Posts
Default

With our 6000w gen I noticed my govenor was set to full throttle. with my load, I was able reduce the setback and ensured the voltage was not lower than 230v on the meter. Lowered the noise quite a bit since it wasnt running wide open. I also dont run my gen at night and restart it early am to get the heat/water back running.
welchislandman is offline   Reply With Quote
Old 11-07-2011, 01:34 PM   #7
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Default

Quote:
Originally Posted by AB_Monterey View Post
Replace that cheap little muffler that it came with.

EEKS, looks to me as if that maybe running in a closed or partially closed area.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 11-07-2011, 02:14 PM   #8
TOAD
Senior Member
 
TOAD's Avatar
 
Join Date: Jun 2009
Location: Soon to be Moultonboro
Posts: 258
Thanks: 1
Thanked 81 Times in 34 Posts
Default

Diesel work every time.

__________________
"Government is not reason, it is not eloquence, it is force; like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action.....Unknown....but attributed to George Washington
TOAD is offline   Reply With Quote
Old 11-07-2011, 02:57 PM   #9
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default Its quiet when its off

With the temps we had in this outage there was no need to run the gen all night long.Get up a little early,start it up and the house is warm in an hour.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 11-07-2011, 06:11 PM   #10
chunt
Member
 
Join Date: Jan 2005
Posts: 20
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Shouldn't change the governor setting. The motor has to run at multiples of 60 to maintain 60HZ power frequency. Small portable generators typically will run at 3600 rpm to maintain the 60hz power frequency.
chunt is offline   Reply With Quote
Old 11-07-2011, 06:46 PM   #11
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Smile

Quote:
Originally Posted by chunt View Post
Shouldn't change the governor setting. The motor has to run at multiples of 60 to maintain 60HZ power frequency. Small portable generators typically will run at 3600 rpm to maintain the 60hz power frequency.
The above is true, however they are producing new generators that reduce the RPM as the load reduces. Knowing this, how does it perform as stated above?? That is just me asking the question as I do not know..
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 11-07-2011, 07:28 PM   #12
brk-lnt
Senior Member
 
brk-lnt's Avatar
 
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
Default

Quote:
Originally Posted by RLW View Post
The above is true, however they are producing new generators that reduce the RPM as the load reduces. Knowing this, how does it perform as stated above?? That is just me asking the question as I do not know..
Some of those are inverter generators. They basically make a lower-voltage that is run through a circuit to great 120V/60Hz power. So, the motor speed does not directly effect the power cycle frequency of the power generated.
__________________
[insert witty phrase here]
brk-lnt is offline   Reply With Quote
Old 11-07-2011, 08:41 PM   #13
Blue Thunder
Senior Member
 
Blue Thunder's Avatar
 
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 935
Thanks: 247
Thanked 323 Times in 148 Posts
Default

Quote:
Originally Posted by AB_Monterey View Post
Replace that cheap little muffler that it came with.
Wow...that is really taking a chance...hope you have a CO detector or two.

BT
__________________
" Live for today because yesterday is gone and tomorrow may never come"
Blue Thunder is offline   Reply With Quote
Old 11-07-2011, 09:45 PM   #14
dpg
Senior Member
 
dpg's Avatar
 
Join Date: Apr 2004
Posts: 2,560
Thanks: 149
Thanked 229 Times in 166 Posts
Default

Another way to go a little quiter is spending good money and purchasing a Honda or equivalent. These units are tolerable but will set you back a few thousand dollars.
dpg is offline   Reply With Quote
Old 11-07-2011, 10:29 PM   #15
AB_Monterey
Senior Member
 
AB_Monterey's Avatar
 
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
Default

Boys,

It wasn't running in that location.

AB_Monterey is offline   Reply With Quote
Old 11-08-2011, 04:36 AM   #16
Belmont Resident
Senior Member
 
Belmont Resident's Avatar
 
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 409 Times in 251 Posts
Default Looks like a garage or shed

Lots of folks run them in a garage with the windows open to vent the fumes and reduce the noise.
Belmont Resident is offline   Reply With Quote
Old 11-08-2011, 06:55 AM   #17
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Smile

Quote:
Originally Posted by Belmont Resident View Post
Lots of folks run them in a garage with the windows open to vent the fumes and reduce the noise.
That to is an extremely dangerous idea. You heard the story on the news last week where a family was over come from a generator exhaust that went into the home through a broken window in the basement. Yep, the generator was outside the house in wide open air space not a location with windows and doors open.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 11-08-2011, 07:05 AM   #18
Blue Thunder
Senior Member
 
Blue Thunder's Avatar
 
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 935
Thanks: 247
Thanked 323 Times in 148 Posts
Default

Quote:
Originally Posted by Belmont Resident View Post
Lots of folks run them in a garage with the windows open to vent the fumes and reduce the noise.
Maybe they do but it is extremely foolish and dangerous to do so.

BT
__________________
" Live for today because yesterday is gone and tomorrow may never come"
Blue Thunder is offline   Reply With Quote
Old 11-08-2011, 08:11 AM   #19
Rolie
Senior Member
 
Rolie's Avatar
 
Join Date: Apr 2004
Posts: 57
Thanks: 4
Thanked 7 Times in 4 Posts
Default Fumes

Quote:
Originally Posted by Belmont Resident View Post
Lots of folks run them in a garage with the windows open to vent the fumes and reduce the noise.
If the garage is attached to the house, they won't do that too many times..maybe even just once!
Rolie is offline   Reply With Quote
Old 11-08-2011, 08:39 AM   #20
AB_Monterey
Senior Member
 
AB_Monterey's Avatar
 
Join Date: Aug 2008
Location: Alton Bay
Posts: 293
Thanks: 86
Thanked 78 Times in 49 Posts
Default

That's a detached shed btw.

But with that car muffler on there (got it at the dump), that thing is QUIET.
AB_Monterey is offline   Reply With Quote
Old 11-08-2011, 12:48 PM   #21
pkadventures
Junior Member
 
Join Date: Jun 2010
Posts: 11
Thanks: 4
Thanked 0 Times in 0 Posts
Default Clarification from OP

Interesting discussion and certainly safety trumps noise in our priorities!

To clarify our generator situation, it is full house disconnect located in the yard outside our house. We live in the house year round but part-time. In our research we found a company (Acoustiblok out of Florida - primarily industrial applications) that sells sound absorbing panels. They sent us a picture of a solid fence with their panels on the inside surrounding the four sides of a residential generator. Something we are considering.

Thanks for the suggestions, of all kinds!
pkadventures is offline   Reply With Quote
Old 11-08-2011, 02:47 PM   #22
MAXUM
Senior Member
 
MAXUM's Avatar
 
Join Date: Apr 2004
Location: Kuna ID
Posts: 2,755
Thanks: 246
Thanked 1,942 Times in 802 Posts
Default

Quote:
Originally Posted by AB_Monterey View Post
That's a detached shed btw.

But with that car muffler on there (got it at the dump), that thing is QUIET.
That have a nice pimped out chrome tip on it?
MAXUM is offline   Reply With Quote
Old 11-08-2011, 03:05 PM   #23
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

I would have to assume that BR was talking about a detached garage and or shed. Never run one in an attached garage or garage under even with the doors open. If its really stormy out I have enough wire to reach my detached shed(75 ft) away. I just face the exhaust out the door and don't spend any time in there during or after for a few days.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 11-08-2011, 05:20 PM   #24
Belmont Resident
Senior Member
 
Belmont Resident's Avatar
 
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 409 Times in 251 Posts
Default Yes siksukr I was.

I honestly did believe anyone would think otherwise, but I guess I was wrong.
I know of several people who have their transfer switch located inside their garage or run them inside the garage with extension cords going into the house. This allows the security of having the generator inside instead of outside where it can be stolen as many have been.
Belmont Resident is offline   Reply With Quote
Old 11-08-2011, 07:03 PM   #25
MarkinNH
Senior Member
 
Join Date: Mar 2010
Posts: 392
Thanks: 177
Thanked 146 Times in 76 Posts
Default

Quote:
Originally Posted by Belmont Resident View Post
I honestly did believe anyone would think otherwise, but I guess I was wrong.
I know of several people who have their transfer switch located inside their garage or run them inside the garage with extension cords going into the house. This allows the security of having the generator inside instead of outside where it can be stolen as many have been.
It is a very doable scenario IMO. All a person needs to do is to use some Common Sense. Proper exhaust, proper fresh air ventilation, regular maintenance and inspections to insure the above and did I mention common sense.
I know of several propane fired standby generators that are in enclosed buildings, these generators have been there for Years without any issues.
Unfortunately the most important key ingredient, Common Sense is severely lacking in todays society
MarkinNH is offline   Reply With Quote
The Following User Says Thank You to MarkinNH For This Useful Post:
Belmont Resident (11-09-2011)
Old 11-09-2011, 06:02 AM   #26
brk-lnt
Senior Member
 
brk-lnt's Avatar
 
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
Default

Quote:
Originally Posted by MarkinNH View Post
I know of several propane fired standby generators that are in enclosed buildings, these generators have been there for Years without any issues.
Propane is way different than petroleum or diesel generators. Those can be safely run in occupied spaces with far less issues. That's why you see forklifts in warehouses running on propane, not diesel...

A gas/diesel genset in an enclosed space operated by a homeowner is a recipe for death, especially if that enclosed space has any ability to exchange air with a living space.
__________________
[insert witty phrase here]
brk-lnt is offline   Reply With Quote
Old 11-09-2011, 07:22 AM   #27
MarkinNH
Senior Member
 
Join Date: Mar 2010
Posts: 392
Thanks: 177
Thanked 146 Times in 76 Posts
Default

Quote:
Originally Posted by brk-lnt View Post
A gas/diesel genset in an enclosed space operated by a homeowner is a recipe for death, especially if that enclosed space has any ability to exchange air with a living space.
This is where the use of Common Sense needs to come into play.
MarkinNH is offline   Reply With Quote
Old 11-09-2011, 07:57 AM   #28
Kamper
Senior Member
 
Kamper's Avatar
 
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,296
Thanks: 67
Thanked 166 Times in 126 Posts
Default

Quote:
Originally Posted by brk-lnt View Post
Propane is way different than petroleum or diesel generators. Those can be safely run in occupied spaces with far less issues. That's why you see forklifts in warehouses running on propane, not diesel...
...
I always thought those things ran on butane. I'm pretty sure propane does produce carbon-monoxide. There are catalytic heaters that use propane that can be used indoors but motors can be hazardous.
Kamper is offline   Reply With Quote
Old 11-09-2011, 08:47 AM   #29
Blue Thunder
Senior Member
 
Blue Thunder's Avatar
 
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 935
Thanks: 247
Thanked 323 Times in 148 Posts
Default

Quote:
Originally Posted by MarkinNH View Post
This is where the use of Common Sense needs to come into play.
Common sense is not that common any more.....
__________________
" Live for today because yesterday is gone and tomorrow may never come"
Blue Thunder is offline   Reply With Quote
Old 11-09-2011, 09:35 AM   #30
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Smile

I think we are on this subject, don't you???
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 11-09-2011, 05:30 PM   #31
Belmont Resident
Senior Member
 
Belmont Resident's Avatar
 
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 409 Times in 251 Posts
Default Another thought

Quote:
Originally Posted by MarkinNH View Post
This is where the use of Common Sense needs to come into play.
You could always hook up an exhaust hose and vent it outside of the detatched holding area. Thats what they do in all automobile repair shops.
I do like the idea of the extended muffler because I'll bet the end never even gets warm so you could use just about any hose to vent the exhaust.
Belmont Resident is offline   Reply With Quote
The Following User Says Thank You to Belmont Resident For This Useful Post:
Winnisquamguy (11-11-2011)
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 09:49 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.26940 seconds