Backup Generators
I just bought a Honda 2000i Generator with two 20 Amp 120 volt outlets. (Like your house outlets.) I'm thinking I can PULL (Turn Off) the Main 100 Amp breaker to the street, and back feed my generator IN ..to a normal weatherproof outdoor receptacle on the deck. Then I can supply power (Up to 2000 Watts) to any receptacle in the house. THE ONLY appliance I expect to feed is the refrigerator, and the furnace for Hot Water. (Showers).
Refrigerator, and Furnace. Nothing more. No Freezers, microwaves, electric stoves/ovens/TVs. If this works..I can add something else...until the generator trips out. What do you think..?? NB |
07-31-2012, 06:33 PM | #2 |
Senior Member
Join Date: Apr 2004
Location: formerly Winter Harbor, still Wolfeboro
Posts: 1,135
Thanks: 284
Thanked 480 Times in 271 Posts
|
Backup Generators
This subject was discussed a t l e n g t h a while back, during the days that CateP was posting a lot about moving the NH and buying a house. The subject of generators was extensively discussed, covering every aspect of generators. As I recollect, the overiding tone of the discussions was that generators present too many potential problems, and generally speaking, a homeowner ought to be extremely wary of doing the wiring themselves - leave it to a licensed electrician and check with the local Code Enforcement Officer about specifics. Safety is the absolute overiding criteria to be aware of.
Good luck. |
07-31-2012, 06:39 PM | #3 |
Senior Member
Join Date: Jul 2008
Location: Ruskin FL
Posts: 1,025
Thanks: 187
Thanked 322 Times in 179 Posts
|
Do it the right way. Don't risk the consequences. Have it hooked up by a licensed electrician. You could be liable if the power back feeds to the grid and causes injury.
|
07-31-2012, 06:45 PM | #4 | |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
Quote:
__________________
There is nothing better than living on Alton Mountain & our grand kids visits. |
|
07-31-2012, 06:56 PM | #5 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Thank you RLW. I Will Say This AGAIN..Refridge and Furnace. I know MY limits..and the limits of my proposal. NB
|
Sponsored Links |
|
07-31-2012, 07:38 PM | #6 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
|
The way you are proposing to do it is illegal and dangerous. You need a switch that locks out to prevent back feeding to the grid. Feeding into a normal receptacle means your cable would be bass ackwards. If you are handy, Lowe's sells a transfer switch that is relatively easy to install and should be legal. There are many safe solutions to this, what you propose is not safe and you need to think down the line where perhaps someone who didn't understand the issues tried to use your system when you weren't around.
|
07-31-2012, 07:42 PM | #7 | |
Senior Member
Join Date: Dec 2010
Location: Winnisquam, NH
Posts: 613
Thanks: 419
Thanked 163 Times in 115 Posts
|
Quote:
__________________
"I'd rather be ridin than rolling" |
|
07-31-2012, 07:50 PM | #8 |
Senior Member
Join Date: Jul 2007
Location: Moultonborough
Posts: 3,530
Thanks: 1,570
Thanked 1,601 Times in 821 Posts
|
Interlock
Hi NB,
IMO, the best and most cost effective method is the panel interlock- so simple it makes other solutions look foolish (as long as you understand current draw (amps) in any way). http://www.interlockkit.com/intro2.htm |
07-31-2012, 08:02 PM | #9 |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
Your original proposal is a cheap hack.
A small manual transfer switch is not expensive, and is very easy to wire in. Going the simple transfer switch route also gives you a very clear indication of when power is restored to your house, because your other lights/devices will come back to life. Pulling or flipping the main breaker makes it much harder to know when power is fully restored (especially if it happens in the middle of the night), and increases the probability that you cause damage to yourself, your generator, or your appliances at some point. There is also the possibility that you injure a line worker, though it's much less likely. If you don't understand the transfer switch concept, PM me and I can give you more info. Or, you're welcome to stop by my place (in Laconia) and I can show you how to wire it up.
__________________
[insert witty phrase here] |
08-01-2012, 05:56 AM | #10 |
Senior Member
Join Date: Apr 2004
Location: Eastern MA & Frye Island/Sebago Lake, Maine
Posts: 935
Thanks: 247
Thanked 323 Times in 148 Posts
|
NB,
Please don't think that we, as a group, are picking on you. Do yourself a favor and search for that thread we did a few months back. There are many different safe and inexpensive ways to do what you want to do but in my opinion, the one you suggest, is not one of them.... BT
__________________
" Live for today because yesterday is gone and tomorrow may never come" |
08-01-2012, 06:53 AM | #11 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
IMO all receptacles/outlets should have a "ONE WAY STREET-DO NOT ENTER" sign on them.
Why do you think they are called "outlets"? |
08-01-2012, 07:08 AM | #12 |
Senior Member
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
|
NB, here is one of the great threads on the subject that will give you some wonderful tips on you endeavors with the generator. Hope it helps.
http://www.winnipesaukee.com/forums/...ght=generators
__________________
There is nothing better than living on Alton Mountain & our grand kids visits. |
08-01-2012, 09:03 AM | #13 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Thanks guys: I get it. Maybe three years ago, my main breaker panel was replaced because after 30+ years, ..my insurance company said it was dangerous. While the electrician was here, I asked him about transfer switches. He quoted me about $600. to add it on.
I have no problem with paying an electrician to do it. However, the transfer switch AND plug would be located just inside..OR outside the garage door....The main panel is just inside the door, so the generator wound have to be outside the door. Thats right on the street. Generator would disappear in a heartbeat...It's such a NICE little generator, expensive..and Very Quiet and VERY Portable. The deck where I want to locate the generator is just outside the dining room french doors where I can keep an eye on it..and the deck is not accessible from the ground without a ladder. Based on your input, I WILL look into other options. NB PS: Now I'll go check out that other thread. EDIT: I just finished the thread noted above. Very sobering. I've got a call in to the "Electrician" that replaced my old panel. Last edited by NoBozo; 08-01-2012 at 10:28 AM. |
08-01-2012, 09:24 AM | #14 |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
It's also relatively easy to have the generator power input be remote from the transfer panel/switch. Depending on the distance, it would determine what gauge of wire you need.
So, you can have the generator on the back deck in operation, have a proper hook up outlet for it right there, and then have the transfer switch next to your main panel.
__________________
[insert witty phrase here] |
08-01-2012, 10:52 AM | #15 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
Voltage loss in a wire is synonymous to pressure loss in a pipe. Electric current flows in a wire, just like water in a pipe, and creates a loss. The loss is a function of: The diameter of the wire - The smaller the diameter, the larger the loss. The length of the wire - The longer the wire, the larger the loss. The type of metal used in the wire - The higher the resistance, the larger the loss. Copper and Aluminum wires are the most common types, with copper having the lower resistance. Voltage Loss is calculated using "OHM'S LAW", as follows: E = IR Where: E is the Voltage Loss, in volts I is the current flowing through the wire, in amperes R is the resistance of the wire, in ohms |
|
08-01-2012, 12:01 PM | #16 |
Senior Member
Join Date: Apr 2004
Location: North Reading, MA and South Down Shores
Posts: 850
Thanks: 57
Thanked 183 Times in 114 Posts
|
There are two issues
First, the losses in the cable reduce the overall available power to load (as pointed out in the prior post). Second, the power goes to heat and too small gauged wire can be a fire hazard. The provided link gives you the resistance of various gauge wire over 1000 feet. Nominally, at 2000 watts the maximum current would be about 18 amps...round up to 20 amps.
Anything larger than 16 gauge will handle the current, but the resistance is 4 ohms. This means that the voltage (V=IR) would be reduced 80 volts across the cable and the power dissipation would be (P=VA) 1600 watts. Not a good day. 0 gauge has a resistance of .0983 ohms for 1000 feet and the voltage drop would be 2 volts, power loss would be 40 watts. Clearly, you may not need 1000 feet and the numbers reduce proportionately with reduction in length. I absolutely agree with the prior posts regarding the hookup. I had an electrician install a manual transfer switch. The switch allows me to decide what distribution to power. In addition, it guarantees that I will not back drive the grid and create a hazard for line crew etc... I picked up a 6500 troy built generator for about $900 which will keep my house reasonably covered. http://hyperphysics.phy-astr.gsu.edu...es/wirega.html |
The Following User Says Thank You to jetskier For This Useful Post: | ||
Rusty (08-01-2012) |
08-01-2012, 06:36 PM | #17 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Update
Based on Everyones input HERE..and the old thread on the same subject.. I decided NOT to do my Jury Rig. Today I returned my new Honda EU2000i for the Honda EU2000i "Companion" which has a 30 Amp 125 Volt Locking Connector.
My electrician does not like the 30 amp..125 volt (Twist Lock) output connector. He would prefer a 30 Amp 125/250 Volt connector. Something about phases. Above my paygrade. NOT available at 2000 watts. My electrical contractor says he can Make It Work for $450/500...Hardware and Labor. I'm going with that. He's coming out Friday to have a look. I could make my jury rig work..BUT...if I Croak..my wife would be left in the learch. She is not as mechanically/electrically competent as I am. Thanks guys: NB |
08-02-2012, 04:54 AM | #18 | |
Senior Member
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 409 Times in 251 Posts
|
Long time!
Quote:
__________________
"better to have a short life that is full of what you like doing, then a long life spent in a miserable way.." |
|
08-02-2012, 05:40 AM | #19 | |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
Quote:
For the type of transfer switch you'll likely end up with, I don't think a generator capable of 240VAC/dual phase would have made much difference in the wiring. Everything is still getting pulled over to a new sub-panel anyway.
__________________
[insert witty phrase here] |
|
08-02-2012, 07:05 AM | #20 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
Anyway, glad that you are not going into an outlet (one way street) to get your electrical needs. |
|
08-02-2012, 07:21 AM | #21 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Electricity could care less which way it travels...to or from an outlet.The only concern is the amps(load) and the wire size.If your outlet circuit is a 20 amp breaker and the gen only puts out 20 then the protection will work just fine.The main concern I have with backfeeding through an outlet(and I've done it) is twofold.You need to make a suicide cord meaning having a plug on both ends.?The danger is obvious one if grabs on to the blades while the other end is energized.The other is backfeeding to the main grid.I backfeed directly to my main panel through a double pole breaker.I have since installed a simple device that won't let you turn that breaker on until the main is off.Very inexpensive and perfectly code acceptable.
__________________
SIKSUKR |
The Following User Says Thank You to SIKSUKR For This Useful Post: | ||
VitaBene (08-05-2012) |
08-06-2012, 07:00 AM | #22 |
Senior Member
Join Date: Apr 2004
Posts: 2,560
Thanks: 149
Thanked 229 Times in 166 Posts
|
Who makes the quietest generator? Anyone own a "quiet model" they're happy with? I have a neighbor in ma with a Home Depot special that could wake the dead.
|
08-06-2012, 07:34 AM | #23 | |
Senior Member
Join Date: Mar 2008
Location: Welch Island and West Alton
Posts: 3,216
Thanks: 1,172
Thanked 2,000 Times in 914 Posts
|
Quote:
The furnace is operated through a properly wired transfer switch. http://www.reliancecontrols.com/Prod...il.aspx?TF151W The other items are operated via extension cords. The 2000i is very quiet. |
|
The Following User Says Thank You to Slickcraft For This Useful Post: | ||
NoBozo (08-06-2012) |
08-06-2012, 06:21 PM | #24 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Thanks Slickcraft for that link. I spent some time looking at the website. Very informative....Also.. that you have a Honda 2000i and it works fine for more stuff than I would have thought.
I'm looking at the Reliance 30114a Transfer Switch that can supply 4 circuits. I could wire the switch YOU have myself..BUT, but would not feel comfortable going beyond that. (enter An electricion) I would like to have the 4 circuit upgrade so my wife can do it on her own later...and get a couple more circuits. I swapped my new Honda 2000i back for the 2000i "Companion" last weekend so I'm now committed to that. The "Companion" has ONE 30 Amp 125 Volt twist/lock conector (L5-30), and ONE 20Amp 125 volt (5-20)...Ie: a normal three prong plug that everyone is familiar with. The basic 2000i has TWO 5-20 connectors. The 30114a ...4 circuit switch is the only one that has a L5-30 connector..and fits the relatively LOW output of the 2000i. NB |
08-07-2012, 09:32 AM | #25 |
Senior Member
Join Date: Jul 2007
Location: Moultonborough
Posts: 3,530
Thanks: 1,570
Thanked 1,601 Times in 821 Posts
|
I would still feed it in through a 30A breaker with an interlock as noted in an earlier post. Then you can pick and choose what you want to run.
I am going with a 15KW PTO driven generator that will be powered by my Kubota L3430 tractor (35 HP at the engine around 30 at the PTO). I am so afraid of gas powered gensets with this ethanol gas we are getting now. |
08-07-2012, 02:23 PM | #26 | |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Quote:
__________________
SIKSUKR |
|
08-11-2012, 05:28 PM | #27 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,296
Thanks: 67
Thanked 166 Times in 126 Posts
|
I just found this tutorial on transfer switches. It's a series of instructional videos. I have not watched it all just peeked at the start of a couple sections.
http://www.reliancecontrols.com/Stre...Player_T1.aspx |
08-12-2012, 05:44 AM | #28 | |
Senior Member
Join Date: Jul 2008
Location: Ruskin FL
Posts: 1,025
Thanks: 187
Thanked 322 Times in 179 Posts
|
Quote:
My generator is not a Honda, but it does have a 319cc Honda motor. I wish I could find a replacement muffler that is quieter than the one it came with. |
|
08-12-2012, 09:15 AM | #29 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,296
Thanks: 67
Thanked 166 Times in 126 Posts
|
|
08-12-2012, 06:55 PM | #30 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
I just saw a "Harbor Freight" ad for a 900 Watt gas generator for $89.99. How can you go wrong..? NB
|
02-09-2013, 08:54 PM | #31 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Update
I originally intended to switch OFF the MAIN feed breaker from the street and back feed the power from my generator into the house via a convenient receptacle. I was talked out of that. I Preferred to do the job right. So I called an electrician who I have used before. He didn't seem interested in the job. OH Well.
So much for my support of local business. I figured it wasn't any big deal. I'll figure it out IF it happens again..probably next decade....we rarely lose power here. Today we had a freakin blizzard and the power went out for 19 hours. The temp outside was 22 F. The temp in the house went down to 48. The local weather said tonight (Sat) the temp outside would go down to 8 degrees. I'm getting desperate. BEST.......I didn't want to do this..I Switched OFF the Main Breaker from the street and Back Fed the power from my 2000 watt Honda generator into the house. It worked..EXCEPT only to certain circuits. I WANTED the Furnace and the Fridge. NO deal. I got lights in some parts of the house but not the TWO appliances I wanted. The work room where the furnace is, had lights....but the furnace didn't have power....different circuit I guess. I'm not an electrician. GOOD NEWS: The power came back on about 4:30 this afternoon. Temp outside is NOW 18.1 and inside is NOW up to 63.7. More thought required. NB |
02-09-2013, 09:07 PM | #32 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
|
NB, this is similar to the switch I installed, if you are comfortable around the panel, it isn't that hard to install. The switch I have uses a remote receptacle that I have outside next to my garage. Check it out, but if you have any doubt, pay someone, it's not a big job.
http://www.reliancecontrols.com/Docu...structions.pdf |
02-09-2013, 09:23 PM | #33 | |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Quote:
|
|
02-10-2013, 08:12 AM | #34 |
Senior Member
Join Date: Jul 2007
Location: Lakes Region
Posts: 1,321
Thanks: 282
Thanked 287 Times in 169 Posts
|
220 ?
I sincerely hope you were feeding a 220V receptacle, including neutral/ground. Otherwise, 220 appliances would feed the other leg of your breaker box, but series them, giving you varying voltage (depending on what appliances were on). I'm sure you are aware of this, but as an engineer, I just had to speak out
Last edited by wifi; 02-10-2013 at 08:57 AM. |
02-10-2013, 09:09 AM | #35 | |
Senior Member
Join Date: Dec 2010
Location: Holden, MA
Posts: 80
Thanks: 14
Thanked 26 Times in 18 Posts
|
Quote:
The Honda 3000 is ultra quiet, and gives you an additional 1000 watts of power over the 2000. I wouldn't mind picking one up. The fuel usage is also a huge difference between the hondas and the big-framed units. I use 1-2 gallons to get 16 hours, vs. most generators that I have seen run 7-8 gallons for the same time. Figure that out for a long-duration event.
__________________
Gary and Diane 290 Fiesta Vee "Nauti Bonnie" |
|
02-10-2013, 10:04 AM | #36 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
However if you must do it that way then I suggest that you turn all the breakers off before starting your generator. Then after you start your generator turn on the 120v breakers one at a time that you want to use. That way you don't over load your generator if one of the circuits take an initial high surge.
__________________
It's never crowded along the extra mile. |
|
02-10-2013, 06:53 PM | #37 | |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
Some Confusing Discussion
Quote:
For simplicity, a row is horizontal and a column is vertical. The typical panel has two 110 v feeds; say Leg A and Leg B. Your Breaker "Space" Nos 1, 2, 3, 4, 5, 6, 7, 8, ... (as numbered/stamped on your panel) are fed by Leg A, B, B, A, A, B, B, A, ... So looking at the left side (column) of breaker spaces going top to bottom would be fed by Leg A, B, A, B, A, B, A, B, ...and the right side (column) of breaker spaces going top to bottom would be fed by Leg B, A, B, A, B, A, B, A, ... Basically, no adjacent breaker spaces (L/R, above/below) are fed from different legs. As can be seen, a 220 v breaker takes up two above/below spaces. I'm just trying to clarify what gslpro is trying to describe. I'm fine with his discussion. Since I have a 220 v table saw in my shop, I just back feed my panel using that receptacle using a 220 v "widowmaker". My wires are sized such that my table saw breaker will adequately protect them. Something to consider if you're feeding through a 20 A 110 v breaker with a cord capable of only delivering 15 A, unless the generator has 15 A overload protection. If this is difficult to follow this, I suggest that you shouldn't be back feeding. As RLW posted earlier, this link is innformative regarding backup generators: http://www.winnipesaukee.com/forums/...ght=generators Good luck. Last edited by Mirror Lake's BB; 02-10-2013 at 07:04 PM. Reason: Added thread link |
|
02-10-2013, 07:19 PM | #38 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
gslpro was right when he said row one is fed by line 1, and row two is fed by line 2 etc. I recommend you shouldn't do any work on your electrical panel until you understand how it is hooked up.
__________________
It's never crowded along the extra mile. |
|
02-10-2013, 07:56 PM | #39 |
Senior Member
Join Date: Aug 2012
Posts: 82
Thanks: 4
Thanked 18 Times in 13 Posts
|
Rusty, Mirror Lakes is correct. On one side of a panel every other breaker is fed by the same line. That is how you are able feed a 240 volt circuit on one side of the panel.
|
02-10-2013, 08:03 PM | #40 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
|
In this case a picture is worth a thousand rules, but I didn't even bother looking for one because the 100kb limit tucks it to me every time.....
|
02-10-2013, 08:05 PM | #41 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Thanks guys for your input. My atitude is: You have ONE chance to get it Wrong. If you pick the wrong chance..YOU May be dead. I have done my own wireing in the house over 34 years...BUT This situation is different.
What you all are describing is Above my paygrade. AND I no longer trust contractors...what else is new...NB |
02-10-2013, 08:07 PM | #42 | |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
Didn't Say What Dinner Was, Did I?
Quote:
That is correct and glad you posted your response quickly for all those following. It has been some time since I took my front cover off my panel and my memory didn't do me any favors. But there is a reason I got confused (age also has something to do with it). I check this anytime I would do work at my panel and should have verified this prior to posting. But I rushed in order to make dinner; baked crow. I apologize to all. Last edited by Mirror Lake's BB; 02-10-2013 at 08:10 PM. Reason: Grammar |
|
02-10-2013, 08:53 PM | #43 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
NoBozo, If I was your neighbor I would hook up a single circuit transfer switch to your panel for you...no charge...I have one kicking around in my garage. I say single circuit because you only have a 2000w generator. They are made to hook to your furnace but I can hook it to your panel to feed the line that your furnace is on. http://www.northerntool.com/shop/too...Fcme4Aod0yYAwA
__________________
It's never crowded along the extra mile. |
|
The Following User Says Thank You to Rusty For This Useful Post: | ||
NoBozo (02-11-2013) |
02-11-2013, 06:03 AM | #44 | |
Senior Member
Join Date: Jan 2005
Location: Florida (Sebring & Keys), Wolfeboro
Posts: 5,788
Thanks: 2,084
Thanked 742 Times in 532 Posts
|
Attached, How? Dunno...
Quote:
Upon setting up, he takes a straight pipe, attaches it onto the exhaust and runs it straight up above the roofline of his RV. The only noise is the normal operating sounds of the engine. |
|
02-11-2013, 09:55 AM | #45 | |
Senior Member
Join Date: Jan 2010
Posts: 250
Thanks: 55
Thanked 61 Times in 44 Posts
|
Quote:
|
|
02-11-2013, 11:03 AM | #46 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
This is not rocket science people. If your generator can supply 220/240 volts then it is a very easy connection. I use a double pole breaker just like all of you have in your panel. I have a twist lock receptacle next to my panel that is fed from that breaker. My cord goes to my gen and to the recep. Simply keep that breaker in the off position, start your generator, turn off your main breaker and turn on the double pole to that receptacle. Viola, your whole panel is energized. If you have a large load like an electric h2o heater or the like then shut that off at the panel. In my case my hot water is from my boiler and the only other real loads are from my shallow well pump and my fridge. I never shut any breakers off and my 5000 watt works fantastic for the following...Water pump, fridge, boiler, large screen tv's and any lights I need.
__________________
SIKSUKR Last edited by SIKSUKR; 02-11-2013 at 02:08 PM. |
02-11-2013, 11:57 AM | #47 |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
220/240 Amps?
SIKSUKR
I don't want to eat crow again but I believe you meant 220/240 "volts". If I'm wrong on this, I'll have to hand in my forum permit privileges. |
02-11-2013, 01:32 PM | #48 | |
Senior Member
Join Date: Jul 2008
Location: Ruskin FL
Posts: 1,025
Thanks: 187
Thanked 322 Times in 179 Posts
|
Quote:
|
|
02-11-2013, 02:08 PM | #49 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Sorry on the volts. As you can see I'm not a rocket scientist. Folks, it really is a very simple install. I now have a very plain plate that I made which doesn't allow you to energize the panel until you shut the main breaker off. Totally legit and to code.
Check the photo out on this website and you'll see how simple they are. http://www.interlockkit.com/?gclid=C...FUKd4AodnmQAmg
__________________
SIKSUKR |
02-11-2013, 04:33 PM | #50 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
I installed a 6 circuit manual transfer switch primarily for ease of use by my wife. I clearly marked the six circuits on the transfer switch so that my wife knows what will be powered. She only has to flip the switches from “Line” to “Gen”. Also she doesn't have to touch the main panel at all to throw the mains or shut off undesired circuits. It couldn't be simpler for her, and that makes it more likely for her to use the generator if I’m not around.
I gave my wife the choice of an interlock or transfer switch and she picked the transfer switch. Personally I like the interlock kit because you can power your whole house with it if you have a big enough generator. One thing to remember is that with the interlock kit you have to make circuit 2 and 4 dedicated for the kit which means you have to have space available for the kit.
__________________
It's never crowded along the extra mile. |
02-11-2013, 05:00 PM | #51 |
Senior Member
Join Date: Jan 2006
Posts: 6,405
Thanks: 719
Thanked 1,379 Times in 955 Posts
|
You COULD have made it easier for her, Rusty. You could have had it transfer itself over automatically like mine does for me. I don't have to touch anything.
|
The Following User Says Thank You to tis For This Useful Post: | ||
Rusty (02-11-2013) |
02-11-2013, 05:46 PM | #52 | |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
Illegal, really?
Quote:
|
|
02-11-2013, 06:42 PM | #53 |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
|
Yes, illegal per code, dangerous and huge liability should it kill someone. Essentially what this type of transfer switch does is make the choice of source either-or, basically foolproof. Whereas some of the setups described here will allow you to select both sources, the power company and generator at the same time. This could be disastrous for a number of reasons, first and foremost a lineman working to repair the wiring outside could be killed.
|
02-11-2013, 07:26 PM | #54 |
Senior Member
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
|
In order to make it 'legal' by means of back-feeding the panel (as most are describing above) you need something along these lines...
Available at: http://www.interlockkit.com/ To be honest, unless you go all out and get an automatic switchover generator, I wouldn't do anything else...including the pricey panels which only provide like 6 or so circuits. The aforementioned concept is really easy to install and works well. However keep in mind that many of the portable generators on the market are not suited for use with sensitive electronics. I know of many furnaces with fancy circuits boards being fried because the generator output is not clean enough. |
02-11-2013, 08:20 PM | #55 | |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
Quote:
|
|
02-11-2013, 08:32 PM | #56 | |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Quote:
EDIT: This box would ONLY serve the furnace. The Common extention cord would allow me to serve other appliences...one at a time..as required. |
|
02-11-2013, 09:10 PM | #57 |
Senior Member
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,296
Thanks: 67
Thanked 166 Times in 126 Posts
|
I now have one of those single circuits transfers on my furnace. It was a breeze to install. I actually mounted it near my furnace because it's 1/2 way between my breaker box and the access for my emergency power. I have been told it's supposed to be next to the circuit breaker box so if I ever sell, I'll remove it to avoid making anyone nervous.
Before that, I used a cut-out with a plug end. When I need it I popped the breaker and disconnected the feed at the furnace switch and tied in the cut-out instead of the main feed. I even had it all set up to go in a junction box so I wouldn't have to remember where I put anything. The only thing on that circuit is the furnace and I understand that's the recommended way to hook it up. Everything else gets extension cords but my house is so small it's not a hardship. I may eventually get fancier but I am comfortable working at this level. |
02-11-2013, 10:28 PM | #58 | |
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
|
Quote:
Sometimes illegal, or even work done not per code or even a professional standard can have consequences far beyond a fine from the government. There are no code police running around randomly inspecting electrical panels, so someone could easily get away with taking the cheap way out and never get caught. Unfortunately people who do it this way put their family and other people's family members (linemen to name one) at risk. Not worth it in my humble opinion. |
|
02-12-2013, 08:47 AM | #59 | |
Senior Member
Join Date: Apr 2004
Location: Wayne, PA & Mirror Lake
Posts: 150
Thanks: 116
Thanked 17 Times in 15 Posts
|
Quote:
As far as your continued discussion regarding the dangers especially to others like linemen, I agree but didn't think it was necessary as a response to my question. It certainly is a post worthy on its own. |
|
02-12-2013, 11:15 AM | #60 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Go ahead and spend unnecessary money
I don't know how anything except an auto transfer switch with an auto start gen could be easier than what I described.Post #54 shows exactly the same photo and link that I provided.You only need to switch the main off and switch the gen breaker on.What the heck could be simpler?Some people over think and over react simple concepts.
__________________
SIKSUKR |
The Following User Says Thank You to SIKSUKR For This Useful Post: | ||
HellRaZoR004 (02-12-2013) |
02-12-2013, 01:42 PM | #61 | |
Deceased Member
Join Date: Dec 2004
Location: Moultonboro
Posts: 849
Thanks: 350
Thanked 351 Times in 193 Posts
|
Quote:
I use an Interlock on my panel and it works fine. You can power up the key circuits needed to "weather" the Storm. When laying out the breaker configuration you want to balance the "load" as evenly on L1 and L2. You can see this on the PANEL layout as to how the Furnace is on L1 and the Refrigerator is on L2. Out side of the Well Pump these are the most important Items to have working. |
|
02-12-2013, 03:18 PM | #62 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
Nice job with the PANEL layout on a pdf file, it explains L1 and L2 very well.
__________________
It's never crowded along the extra mile. |
|
02-18-2013, 03:21 PM | #63 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
I think the Honda 2000i Companion would work OK with this Transfer Switch. You have probably already viewed this video about how to hook it up, but if not then take a look at it and you will see that it is easy to do: http://www.reliancecontrols.com/Stre...Player_T1.aspx I think if a Monkey watched the video he could do it...Maybe.
__________________
It's never crowded along the extra mile. |
|
03-03-2013, 05:07 AM | #64 | |
Senior Member
Join Date: Jan 2005
Location: Florida (Sebring & Keys), Wolfeboro
Posts: 5,788
Thanks: 2,084
Thanked 742 Times in 532 Posts
|
Hold that thought...
Quote:
http://winnipesaukee.com/forums/showthread.php?t=14574 Still another way derives from a two-year-old discussion that shows that in the very near future, your electric car can be your home's generator for a couple of days—or with a hybrid vehicle—as long as you have gas (or propane) in the tank. The photograph shows what the charging station looks like in your carpeted garage. But sales are off for the all-electric Nissan Leaf, so a price-drop of $6000 was announced two months ago. The "newest-news", however, is a rumor that Nissan is planning on dropping the battery-only vehicle altogether. That latest blurb is tainted only by the fact that the "info" originated from America's largest exporter of US-made vehicles—BMW. |
|
03-03-2013, 08:49 AM | #65 | |
Senior Member
Join Date: Jan 2003
Location: Alton Bay
Posts: 5,547
Blog Entries: 2
Thanks: 2,397
Thanked 1,918 Times in 1,061 Posts
|
Me, I am scared to death about electricity, but...
Quote:
I must agree that even with my great fear, even I would feel confident in performing this installation. Thanks for sharing. Oh, and it looks like the model in the video was the 30216a with an MSRP of about $380 vs $200 for the 30114a
__________________
I Live Here... I am always UPTHESAUKEE !!!! |
|
03-03-2013, 09:05 AM | #66 | |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
Quote:
But, no, you do not tape wire nuts.
__________________
[insert witty phrase here] |
|
03-03-2013, 11:40 AM | #67 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
The 30114a is 4 circuit and the 30116a is 6 circuit. Hence the 4 and 6 at the end of the number.
__________________
It's never crowded along the extra mile. |
|
The Following User Says Thank You to Rusty For This Useful Post: | ||
upthesaukee (03-03-2013) |
03-03-2013, 02:05 PM | #68 | |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
Quote:
Electrical tape is notorious for shrinking over time or with heat, and loosing its stick. You come back to a gooey mess if you need to service the work later. When was the last time you looked at the work of a professional electrician and saw taped wire nuts?
__________________
[insert witty phrase here] |
|
The Following 3 Users Say Thank You to brk-lnt For This Useful Post: | ||
03-03-2013, 05:08 PM | #69 | |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Quote:
|
|
The Following User Says Thank You to NoBozo For This Useful Post: | ||
Rusty (03-04-2013) |
03-03-2013, 07:34 PM | #70 | |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Quote:
http://www.reliancecontrols.com/Prod...il.aspx?TF151W EDIT: I just ordered it: AMAZON: $69.99. Watch out for Rusty: He's PUSHY... Last edited by NoBozo; 03-03-2013 at 08:22 PM. |
|
The Following User Says Thank You to NoBozo For This Useful Post: | ||
Rusty (03-04-2013) |
03-04-2013, 09:43 AM | #71 |
Senior Member
Join Date: Aug 2007
Location: South Down Shores
Posts: 1,937
Thanks: 532
Thanked 568 Times in 334 Posts
|
It's not against code, it's just (generally) a sign of amateur/DIY work.
__________________
[insert witty phrase here] |
03-04-2013, 11:18 AM | #72 |
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Yout wire nuts should never loosen up by just bending wires and stuffing them in the box.Scary stuff.This should tell you that your not installing them properly.First,make sure both(or 3)(no more than 3) of the wires are stripped the same length and will be encased in the nut after tightening.Have them all nice and straight and all standing right next to each other and especially,have all the ends at the same position.Twist your nut while firmly holding all the wires and don't let go of the wires until your have the nut pretty secure.Twist it as hard as you can by hand until the wires actually start to twist.A couple electricians I know will actually finish twisting larger gauge (12,10 and up) with lineman pliers.Lastly,pull on all each wire
to see if it stays connected.I've had a more than a few pull out when I thought they were tight.That loose wire is exactly what you don't want and this is an easy check to see that they are securely fastened.
__________________
SIKSUKR |
03-04-2013, 01:27 PM | #73 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
OK, you win.
__________________
It's never crowded along the extra mile. Last edited by Rusty; 03-07-2013 at 08:16 PM. |
03-04-2013, 07:18 PM | #74 |
Senior Member
Join Date: Jun 2009
Posts: 118
Thanks: 0
Thanked 14 Times in 11 Posts
|
If you twist enough wire nuts, you can usually feel a bad connection. Either the wire nut will feel tight sooner than it should or it will not tighten. In either case, take the connection apart and remake it. There is really no need to tape a properly made connection.
|
03-05-2013, 06:08 PM | #75 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Update
The transfer switch came in today from Amazon. The three prong recessed (male) recepticle was seperate and not installed in the transfer switch box. The instructions regarding this were non existant.
Inside the box were three pigtails..stripped on the ends: Black, White and Green that are intended to be wired to the back of the male recessed three prong recepticle which will be installed in the front of the box. SO: Obviously the Green wire is Ground. and can be inserted into the Green terminal in the back of the three prong recessed recepticle. What about the Black and White pigtails..?? Which color (B or W) goes on "which flat blade" .. of the male (Recessed) three prong recepticle..?? Monkey wants another banana. NB |
03-05-2013, 06:17 PM | #76 |
Senior Member
Join Date: Jul 2007
Location: Lakes Region
Posts: 1,321
Thanks: 282
Thanked 287 Times in 169 Posts
|
In AC systems, white is neutral and goes to the wider prong and black is hot and goes to the smaller prong.
|
03-05-2013, 07:20 PM | #77 |
Senior Member
Join Date: Aug 2006
Location: Moultonborough, NH
Posts: 484
Thanks: 89
Thanked 138 Times in 72 Posts
|
Usually there is a gold terminal and a silver terminal. Black goes to the gold terminal if there is one.
|
03-05-2013, 08:29 PM | #78 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
the brass screw is for the hot wire (black) and silver screw is for the neutral wire (white).
__________________
It's never crowded along the extra mile. Last edited by Rusty; 03-07-2013 at 08:00 PM. |
03-05-2013, 08:35 PM | #79 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
No Silver or Gold terminals on the Leviton connector supplied with the transfer switch. Just the Green. NB
EDIT: See post #85. Last edited by NoBozo; 03-06-2013 at 11:06 AM. |
03-05-2013, 08:51 PM | #80 | |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
Quote:
__________________
It's never crowded along the extra mile. Last edited by Rusty; 03-05-2013 at 09:57 PM. Reason: clarified the terminal and added blade color |
|
03-06-2013, 07:01 AM | #81 |
Senior Member
Join Date: Jul 2008
Location: Ruskin FL
Posts: 1,025
Thanks: 187
Thanked 322 Times in 179 Posts
|
Some good advice here...and some bad advice too. How do you choose?
Best advice....mount all the hardware, run all the wires...then call a licensed electrician to make the final connections. Could end up being the best $100 or so you spend. |
03-06-2013, 10:03 AM | #82 | |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
Quote:
|
|
03-06-2013, 10:34 AM | #83 |
Senior Member
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
|
You are correct.
__________________
It's never crowded along the extra mile. Last edited by Rusty; 03-07-2013 at 07:54 PM. |
03-06-2013, 10:59 AM | #84 |
Senior Member
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
|
New Update
Thanks guys for the input. I had a closer look this morning. There ARE Gold and Silver terminals. Everything checks out. It's wired correctly. NB
Here is the recepticle used. http://www.leviton.com/OA_HTML/Produ...minisite=10251 |