I need a good electrician to quote me a price to heat a crawl space. 40' x 25' ish. about 4' high but split in two with a wall in the middle. Big hole in the wall to crawl through.
We had been using an electric space heater....240V style garage heater, on one side and a small milk house heater on the other...to heat the space previously. But that to me was not so safe. I certainly do not want to be responsible for a fire, so I need someone to get me some heat under there.
Anyone know anyone?

This is what happened to the cord on the last heater.....See what I mean? This never tripped the breaker! Yikes!
Attached Images
 
Lakesrider is offline   Reply With Quote
Old 11-05-2012, 04:18 PM   #2
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

Probably wasn't overloaded more likely a bad connection due to loose wire or corrosion or wrong wire type for receptacle. Could do it yourself if you are handy.
ITD is online now   Reply With Quote
Old 11-05-2012, 06:37 PM   #3
DickR
Senior Member
 
Join Date: Apr 2008
Location: Moultonborough
Posts: 735
Thanks: 4
Thanked 254 Times in 166 Posts
Default

Yikes is right, with that outlet damage so close to unprotected EPS foam nearby. You might think about protecting that foam with something. Current code says:
"...all foam plastic insulation must be separated from the interior of the building by an approved 15-minute thermal barrier, such as ½-inch gypsum wall board or equivalent material. This thermal barrier may be omitted if certain conditions are met in attics and crawl spaces. Specifically, entry must be restricted to service of utilities AND the foam plastic must be protected from ignition with a code specified material.

Section 316.5.3 of the IRC prescriptively defines the
following six materials as ignition barriers:
• 1½” mineral fiber insulation
• ¼” wood structural panels
• ⅜” particleboard
• ¼” hardboard
• ⅜” gypsum wall board
• 16 mil corrosion resistant steel
DickR is offline   Reply With Quote
Old 11-05-2012, 07:26 PM   #4
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

For the circuit breaker not to trip with a burn like that, there could have been a GFCI receptacle up stream that tripped which in turn shut off the electrical flow. Did you notice that one of your GFCI receptacles had tripped.
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 11-05-2012, 07:49 PM   #5
songkrai
Senior Member
 
Join Date: Dec 2009
Posts: 725
Thanks: 35
Thanked 145 Times in 98 Posts
Default

My "Milkhouse" heater did the same exact thing.

Mine was an older Milkhouse heater. The wire/cord became brittle over the years and a couple of cracks developed on the plastic coating of wire that plugs into outlet.

I used it for years in same place. This fall it worked sometimes. Then stopped working. I thought that the heater was broken. When I looked at plug (behind desk) I viewed same as picture above.

I cut cord/wire and put new plug on heater and it works fine. But it is now in storage as I purchased a new one.
songkrai is offline   Reply With Quote
Sponsored Links
Old 11-06-2012, 09:07 AM   #6
Lakesrider
Senior Member
 
Join Date: Jun 2007
Posts: 2,129
Thanks: 380
Thanked 1,016 Times in 345 Posts
Default

Quote:
Originally Posted by DickR View Post
Yikes is right, with that outlet damage so close to unprotected EPS foam nearby. You might think about protecting that foam with something. Current code says:
"...all foam plastic insulation must be separated from the interior of the building by an approved 15-minute thermal barrier, such as ½-inch gypsum wall board or equivalent material. This thermal barrier may be omitted if certain conditions are met in attics and crawl spaces. Specifically, entry must be restricted to service of utilities AND the foam plastic must be protected from ignition with a code specified material.

Section 316.5.3 of the IRC prescriptively defines the
following six materials as ignition barriers:
• 1½” mineral fiber insulation
• ¼” wood structural panels
• ⅜” particleboard
• ¼” hardboard
• ⅜” gypsum wall board
• 16 mil corrosion resistant steel
Yeah I know. this is a really old building and that was done way before i started there. I planned to drywall all around the utility section. Access is limited to just me and any service personnel.
It's getting a bit late to wait to get this done.....I'm getting nervous about the pipes.
Lakesrider is offline   Reply With Quote
Old 11-06-2012, 10:06 AM   #7
HellRaZoR004
Senior Member
 
Join Date: May 2012
Location: Litchfield/Gilford
Posts: 828
Thanks: 233
Thanked 224 Times in 131 Posts
Default

Quote:
Originally Posted by Lakesrider View Post
Yeah I know. this is a really old building and that was done way before i started there. I planned to drywall all around the utility section. Access is limited to just me and any service personnel.
It's getting a bit late to wait to get this done.....I'm getting nervous about the pipes.
Yeah - it got cold last night.
HellRaZoR004 is offline   Reply With Quote
Old 11-06-2012, 02:50 PM   #8
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

If that was my setup, here's what I would do. If you don't need to plug an unplug the heater for moving it around purposes I would hard wire it. Very simple actually and you could use that existing box. Cut back the wire to where the insulation is not brittle anymore from the overheating, which is caused by either a loose plug connection or loose wire on the plug itself. Make hard connections with good solid twisting and firmly twisted wire nuts. The less possible loose connections, the better. This is when arcing occurs and in turn what you ended up with assuming all wire is sized properly for that load.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 11-07-2012, 09:52 AM   #9
Lakesrider
Senior Member
 
Join Date: Jun 2007
Posts: 2,129
Thanks: 380
Thanked 1,016 Times in 345 Posts
Default

Well I think I found the issue. It seems the electric space heater was rated at 30amps. Someone cut off the plug and changed it to a 20 amp 240 volt plug. The breakers are only 20amp and the line is a 12/2. So it was overheating the plug I think.....well I know obviously. The last heater was a 5000 watt type. So last night I headed up to the North Conway Lowe's and got a new 4000 watt 20 amp heater. A Farenheat garage heater. I will install it and see how that goes. Most likely keep it on the low setting. I can raise it to the higher setting if it got really cold out like it does sometimes. I just have to remember to do it!
I did put some drywall above the heater to protect that foam. Also after looking around at the foundation it did seem pretty tight. I could not see any light coming through anywhere, so hopefully that is a good thing.
Talk about spider webs in there......yuck!
Lakesrider is offline   Reply With Quote
Old 11-09-2012, 07:20 AM   #10
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

That probably was NOT your problem. If the heater was drawing 30 amps and not tripping the 20 amp breaker, you better look at that breaker asap. If the plug was cut off and a different one installed then most likely the connections were not tight and arcing was occurring. Don't just go plug your your new heater into that receptacle. I assume you changed that one out cuz its toast. More than likely the wires supplying it were overheated also and the insulation damaged. Make sure to cut back to good soft insulation and install the wire to terminals tightly.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
The Following User Says Thank You to SIKSUKR For This Useful Post:
ITD (11-09-2012)
Old 11-09-2012, 08:21 AM   #11
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,860
Thanks: 461
Thanked 666 Times in 366 Posts
Default

I agree with SS on this, that breaker should have tripped if the heater was on full power. I also think there was a loose connection somewhere. I wouldn't trust that breaker knowing this.

I also would have an electric baseboard with a thermostat hard wired in, it might cost a little more up front, but I think having the heater on a thermostat will save you in the long run. I looked for a plug in thermostat for you , but was only able to find 120V.

Good luck.
ITD is online now   Reply With Quote
Old 11-09-2012, 08:35 AM   #12
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by Lakesrider View Post
Well I think I found the issue. It seems the electric space heater was rated at 30amps. Someone cut off the plug and changed it to a 20 amp 240 volt plug. The breakers are only 20amp and the line is a 12/2. So it was overheating the plug I think.....well I know obviously. The last heater was a 5000 watt type. So last night I headed up to the North Conway Lowe's and got a new 4000 watt 20 amp heater. A Farenheat garage heater. I will install it and see how that goes. Most likely keep it on the low setting. I can raise it to the higher setting if it got really cold out like it does sometimes. I just have to remember to do it!
I did put some drywall above the heater to protect that foam. Also after looking around at the foundation it did seem pretty tight. I could not see any light coming through anywhere, so hopefully that is a good thing.
Talk about spider webs in there......yuck!
Am I correct in understanding that you have 12/2 wire going to a 20 amp, 120 volt breaker for your heater?

What is the voltage for the new 4000 watt 20 amp heater that you bought?

I'm a little confused about your statement: "Someone cut off the plug and changed it to a 20 amp 240 volt plug". Was the heater 240 volts?
__________________
It's never crowded along the extra mile.
Rusty is offline   Reply With Quote
Old 11-11-2012, 08:46 AM   #13
Lakesrider
Senior Member
 
Join Date: Jun 2007
Posts: 2,129
Thanks: 380
Thanked 1,016 Times in 345 Posts
Default

Sorry. No. What I had was a 30 amp breaker on a 12/2 wire. Someone installed a 20amp 240V outlet, then cut off the 30 amp plug on the cord and installed a matching 20amp 240V plug. So the plug over-heated and melted. I thought it was a 20 amp dual breaker because it was labeled Basement heater. Well come to find out The 30 amp was on. Not labeled. ( I did relabel everything) I found that out by the tingle in my right arm when I touched the white wire and the ground at the same time. Now I had tested the wires with my meter and got nothing. It seems one side of the 30amp dual was burned out but the other side of it was not.. I bought a new 20 amp ( to replace the 30Amp) dual breaker, new outlet, and installed a 20 amp 4,000 watt heater. It has been running fine for the past few days. I did add drywall to the ceiling for a good portion of the area around the heater too. Nice and warm in there now. I have the heater set to the low setting which is only 9,000 watts.
Lakesrider is offline   Reply With Quote
Old 11-11-2012, 10:07 AM   #14
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by Lakesrider View Post
Sorry. No. What I had was a 30 amp breaker on a 12/2 wire. Someone installed a 20amp 240V outlet, then cut off the 30 amp plug on the cord and installed a matching 20amp 240V plug. So the plug over-heated and melted. I thought it was a 20 amp dual breaker because it was labeled Basement heater. Well come to find out The 30 amp was on. Not labeled. ( I did relabel everything) I found that out by the tingle in my right arm when I touched the white wire and the ground at the same time. Now I had tested the wires with my meter and got nothing. It seems one side of the 30amp dual was burned out but the other side of it was not.. I bought a new 20 amp ( to replace the 30Amp) dual breaker, new outlet, and installed a 20 amp 4,000 watt heater. It has been running fine for the past few days. I did add drywall to the ceiling for a good portion of the area around the heater too. Nice and warm in there now. I have the heater set to the low setting which is only 9,000 watts.
WOW!! 12/2 wire going to a 30 amp dual breaker. You are lucky that the only thing that happened was a burnt outlet.

Now you have a 20 amp dual breaker that goes to your 20 amp 4000 watt heater. So my question is: What do you have hooked to the other side of the dual breaker? Do you have a dual breaker because you ran out of room in your panel for a single pole breaker?
__________________
It's never crowded along the extra mile.

Last edited by Rusty; 11-11-2012 at 10:23 AM. Reason: edited to remove some questions that I had.
Rusty is offline   Reply With Quote
Old 11-11-2012, 03:11 PM   #15
KDL
Senior Member
 
Join Date: Jun 2009
Posts: 118
Thanks: 0
Thanked 14 Times in 11 Posts
Default

I agree, permanently installed baseboard heat would be the way to go. I would install an 8' high density 2500W, or two 5' 1250W units on each side, with it's own thermostat and own 15A 240V circuit. Two of everything would give you redundancy in the unlikely case one would fail.

A 20A circuit for a 4000W heater is under sized, especially for a cord and plug connected heater.
KDL is offline   Reply With Quote
Old 11-12-2012, 02:42 PM   #16
Lakesrider
Senior Member
 
Join Date: Jun 2007
Posts: 2,129
Thanks: 380
Thanked 1,016 Times in 345 Posts
Default

It is what was called for in the instructions. It only draws 16amps at the high setting and I am leaving it on the low 1500 watt setting. Sorry not 9,000 like I posted above.
Been several days and it is still fine.
I won't do anything else to it. I will get a lic electrician if it should need more work.

Can't have a single breaker on 240V. Needs two legs so a double breaker.
Lakesrider is offline   Reply With Quote
Old 11-12-2012, 03:29 PM   #17
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

Double pole breaker.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 12-27-2012, 11:58 AM   #18
willcastner
Junior Member
 
Join Date: Jun 2012
Posts: 13
Thanks: 0
Thanked 1 Time in 1 Post
Default

Looks like you got lucky there. With a crawl space of basement there is a few different ways to insulate. if there are plumbing pipes or heating system down there the walls should be insulated. Many people insulate the ceiling of a basement or crawl. In MOST cases this is the wrong way. By insulatiing the ceiling you are pushing the plumbing and/or heating system out side the heating envelope. This cause efficiency/comfort issues due to unused heatloss from any heatsource and pipes to freeze.

This can be something you can address and often times by fixing eleminate the need for a heater down there all together.
willcastner is offline   Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 08:22 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.25033 seconds