Curious if anyone will be operating their mini spilts for heating this weekend. If so, please let us know how they perform in this weather
Sent from my iPhone using Winnipesaukee Forum mobile app |
![]() |
![]() |
![]() |
#102 |
Senior Member
Join Date: Mar 2008
Location: Welch Island and West Alton
Posts: 3,096
Thanks: 1,102
Thanked 1,881 Times in 863 Posts
|
![]()
Our hyper heat units 100% crossover efficiency is at about 0 deg F and they are good for operation down to minus 13 deg and 85% efficiency. However, when the temp drops below 0 deg I shut them off and switch to oil heat for zones not covered by the pellet stove. So I would not run them this Friday night.
Alan |
![]() |
![]() |
![]() |
#103 | |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,497
Thanks: 2,125
Thanked 4,507 Times in 1,749 Posts
|
![]() Quote:
Will be using again this weekend and I will report back for you. Dan
__________________
It's Always Sunny On Welch Island!! ![]() |
|
![]() |
![]() |
![]() |
#104 | |
Senior Member
Join Date: Jun 2016
Location: Tuftonboro and Sudbury, MA
Posts: 2,030
Thanks: 1,009
Thanked 860 Times in 532 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#105 | |
Senior Member
Join Date: Mar 2008
Location: Welch Island and West Alton
Posts: 3,096
Thanks: 1,102
Thanked 1,881 Times in 863 Posts
|
![]() Quote:
The math is straightforward. At minus 15 deg 85% efficient means 100 watts in gets only 85 watts of heat out. Over 0 deg temp the efficiency is over 100% so the heat pump puts out more watts than what is required to run the unit. The above has nothing to do with comparison with oil heat. That said, the advantage over oil is temp dependent and numbers like 30% are on average. At 10 below zero best to run the oil burner. Alan |
|
![]() |
![]() |
Sponsored Links |
|
![]() |
#106 |
Senior Member
Join Date: Mar 2006
Location: Merrimack and Welch Island
Posts: 3,611
Thanks: 1,053
Thanked 1,356 Times in 875 Posts
|
![]()
With no direct experience, just quotes from vendors, I have the impression that as temperature drops, so does efficiency of the mini-splits. However, that says to me that they don't fail to heat, it just costs more to run them. If the temp drops to 0 F I pay more for oil and the electricity to pump the hot water or hot air around the house. Presumably, I pay more for the mini splits to operate as well, but I can turn down the heat in lesser used rooms and balance things out. Yes ? No?
|
![]() |
![]() |
![]() |
#107 |
Senior Member
Join Date: Jun 2021
Posts: 2,057
Thanks: 2
Thanked 387 Times in 322 Posts
|
![]()
I think it has to do with a drop in the BTU output to the point that the unit cannot keep up regardless of how long it runs.
|
![]() |
![]() |
![]() |
#108 |
Senior Member
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,417
Thanks: 2,993
Thanked 1,062 Times in 763 Posts
|
![]()
I know the efficiency of my condensing gas boiler and how much it cost per btu.
I also know the efficiency of my split system and how much it cost per btu. The efficiency of the mini-split drops as the outside temperature drops. I find the cross-over point. This is where I switch to the more efficient heat. Also, the gas boiler heats up a cold space rather quickly compared to the split system. So I use gas to increase the temperature and switch to the split. An engineer told me that a split is inefficient when trying to raise the temperature of a cold home. It is efficient in maintaining a set temperature. So do some research and use your judgment.
__________________
Someday may never be an actual day. |
![]() |
![]() |
![]() |
#109 |
Senior Member
Join Date: Nov 2010
Posts: 977
Thanks: 16
Thanked 284 Times in 176 Posts
|
![]()
I view so many new homes such as this.
With fancy dormers. With window bottoms so close to the roof. Where do these architects think that the snow and melting snow is going to go? Under dormer windows. |
![]() |
![]() |
![]() |
#110 |
Senior Member
Join Date: Dec 2016
Posts: 1,603
Thanks: 167
Thanked 509 Times in 341 Posts
|
![]()
Called my installer and asked about running my mini split in this cold. I have a 36k btu unit installed with 4 heads. Looking to run only one head. Kids are coming up for the hockey and we need to heat the space we close up for the winter months. I was told the performance will be cut in half, however with only one head running we should have no issues. Turned it on last evening and the space is holding at 62. About 800 sq feet
Sent from my iPhone using Winnipesaukee Forum mobile app |
![]() |
![]() |
![]() |
#111 | |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,497
Thanks: 2,125
Thanked 4,507 Times in 1,749 Posts
|
![]() Quote:
Dan
__________________
It's Always Sunny On Welch Island!! ![]() |
|
![]() |
![]() |
![]() |
#112 |
Senior Member
Join Date: Dec 2016
Posts: 1,603
Thanks: 167
Thanked 509 Times in 341 Posts
|
![]()
Hyper heat, I believe. Good for -10 I was told
Sent from my iPhone using Winnipesaukee Forum mobile app |
![]() |
![]() |
The Following User Says Thank You to WinnisquamZ For This Useful Post: | ||
ishoot308 (02-03-2023) |
![]() |
#113 | |
Senior Member
Join Date: Jun 2016
Location: Tuftonboro and Sudbury, MA
Posts: 2,030
Thanks: 1,009
Thanked 860 Times in 532 Posts
|
![]() Quote:
|
|
![]() |
![]() |
![]() |
#114 | |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,497
Thanks: 2,125
Thanked 4,507 Times in 1,749 Posts
|
![]() Quote:
Dan
__________________
It's Always Sunny On Welch Island!! ![]() |
|
![]() |
![]() |
![]() |
#115 |
Senior Member
Join Date: Jun 2021
Posts: 2,057
Thanks: 2
Thanked 387 Times in 322 Posts
|
![]()
If it put out enough BTUs at the lower efficiency.
|
![]() |
![]() |
![]() |
#116 | |
Senior Member
Join Date: Apr 2008
Location: Moultonborough
Posts: 705
Thanks: 4
Thanked 240 Times in 155 Posts
|
![]() Quote:
That 85% number for the minisplit likely indicates how much of full rated capacity (BTU/hr) is being delivered from a very cold outside temperature. In general, except for some losses along the path, a heat pump delivers as heat all of the electrical energy input to the compressor plus whatever is absorbed from the source (outside air) by the evaporation of refrigerant on the cold (low pressure) side. Thus the COP will always be above 1.0 and substantially so. It should be noted that heat pumps installed in heating climates generally are sized according to the expected heating load at some design minimum heat loss rate, which can be calculated sufficiently well for any house. On the other hand, most fired heat systems installed over the years typically are grossly oversized relative to expected demand, often by a factor of 2 to 4. Such a system has a lot of extra capacity, which leads to short cycling in normal use but which does let a cold house recover rapidly after a power outage or other period of deep setback. In contrast, a properly sized heat pump does not have that huge reserve of overcapacity for rapid recovery. |
|
![]() |
![]() |
The Following User Says Thank You to DickR For This Useful Post: | ||
ishoot308 (02-03-2023) |
![]() |
#117 |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,385
Thanks: 1,750
Thanked 980 Times in 614 Posts
|
![]()
My wood stove has been blasting out heat for two straight days now and I'm just able to keep the house at 68 degrees tonight, and it's a well insulated home. I have oil heat and I don't think that would keep up at these temperatures. I doubt a Mini Split would keep up tonight, it's -12 right now in Meredith.
|
![]() |
![]() |
![]() |
#118 | |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,497
Thanks: 2,125
Thanked 4,507 Times in 1,749 Posts
|
![]() Quote:
Dan
__________________
It's Always Sunny On Welch Island!! ![]() |
|
![]() |
![]() |
The Following 3 Users Say Thank You to ishoot308 For This Useful Post: | ||
![]() |
#119 | |
Senior Member
Join Date: Dec 2016
Posts: 1,603
Thanks: 167
Thanked 509 Times in 341 Posts
|
![]() Quote:
Sent from my iPhone using Winnipesaukee Forum mobile app |
|
![]() |
![]() |
The Following User Says Thank You to WinnisquamZ For This Useful Post: | ||
ishoot308 (02-03-2023) |
![]() |
#120 |
Senior Member
Join Date: Jun 2021
Posts: 2,057
Thanks: 2
Thanked 387 Times in 322 Posts
|
![]()
Good... that means that with any luck the store will be toasty warm when I get in tomorrow.
|
![]() |
![]() |
![]() |
#121 |
Senior Member
Join Date: Dec 2016
Posts: 1,603
Thanks: 167
Thanked 509 Times in 341 Posts
|
![]()
As I have noted in the past. Mini spilts work when left on. Not great at recovery for either heat or ac
Sent from my iPhone using Winnipesaukee Forum mobile app |
![]() |
![]() |
The Following User Says Thank You to WinnisquamZ For This Useful Post: | ||
FlyingScot (02-04-2023) |
![]() |
#122 |
Senior Member
Join Date: Jun 2021
Posts: 2,057
Thanks: 2
Thanked 387 Times in 322 Posts
|
![]()
They held the temperature at the Bristol store...
But the downstairs back up propane-fired heaters are going full bore. |
![]() |
![]() |
![]() |
#123 | |
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 3,385
Thanks: 1,750
Thanked 980 Times in 614 Posts
|
![]() Quote:
![]() I've been thinking of adding mini splits for AC and those days, in the high 40's & 50's, when it's not quite cold enough to light the stove. |
|
![]() |
![]() |
![]() |
#124 | |
Senior Member
Join Date: Feb 2008
Location: Gilford, NH / Welch Island
Posts: 5,497
Thanks: 2,125
Thanked 4,507 Times in 1,749 Posts
|
![]() Quote:
I have mini splits out at my island camp also but not the hyper heat units just standard ones since I only use them for AC but they also kick butt in cooling down the camp on the hottest of days. Dan
__________________
It's Always Sunny On Welch Island!! ![]() |
|
![]() |
![]() |
![]() |
#125 |
Junior Member
Join Date: Jul 2015
Posts: 8
Thanks: 0
Thanked 7 Times in 4 Posts
|
![]()
I stayed up and monitored my Mitsubishi hyper heat heat pumps until 2AM last night and they performed well above my expectations. The specs on the heat pumps say the minimum temperature to make heat is -13. At 1:30AM, it was -17. The thermostat was set at 73 and maintained at 72 most of the day and dropped to 71, then 70 at 1:30 and stayed there. The house was 70 at 7AM this morning when it was -16.
The heat pump was a one to one 18,000 BTU unit that heated the entire downstairs, stairwell hall, upstairs hall and bath, about 850 square feet. I have a second 3 head unit for each bedroom and heated only one bedroom last night with that and it did the job. I have a propane stove in the living room as back up ready to go but it wasn't needed. I had the dogs out at 1AM and those outside units were really working hard. The efficiency of the heat pumps were probably poor compared to oil or natural gas. The only other thing I noticed was the defrost cycles took a lot longer and it took longer for the heat to ramp back up. That was a little scary when the temperature got down below -14, but the heat pumps passed the test. |
![]() |
![]() |
The Following 3 Users Say Thank You to joec For This Useful Post: | ||
![]() |
#126 |
Senior Member
Join Date: Aug 2006
Location: Meredith Bay/MA
Posts: 73
Thanks: 113
Thanked 47 Times in 17 Posts
|
![]()
Meredith about -17, Mitsubishi hyper heat, 5 heads, 42kBTU (2 years old). Monitored on the kumo cloud app from MA. This is for my 2nd floor, heads in 4 bedrooms and a large 40x20x10 room. Probably not a good comparison as the bedrooms open to a loft/great room and receives heat from the 1st floor which is oil boiler, hydro heat. I usually leave the 1st floor at 58 and 2nd floor at 60 but the heads in the bedrooms do not run much.
The large room (no heat from 1st floor) held 60 all night. As much as I like the system, I would have a backup plan. For us we have a propane wood stove in the large room. |
![]() |
![]() |
![]() |