Unhappy Hot Water Baseboard Repair

One zone of our hot water baseboard heating system never gets more than lukewarm even though it's pretty close to the furnace. I suspect that the water is not circulating properly

Anyone care to recommend a plumber/heating contractor who can check it out for me? I'm in the Alton/Gilford area.

Thanks for your help!
Whimsey is offline   Reply With Quote
Old 09-09-2010, 05:40 PM   #2
Comptonbuilder
Member
 
Join Date: Sep 2009
Posts: 33
Thanks: 0
Thanked 3 Times in 3 Posts
Default

I would give Minute Man Plumbing and Heating a call. They do all my new construction and remodeling projects. Their numbers are 603-279-3323 or cell phone 603-387-1476 ask for Phil Brown. They are definately worth the call.

Regards

Scott Compton
Comptonbuilder is offline   Reply With Quote
Old 09-09-2010, 06:56 PM   #3
Belmont Resident
Senior Member
 
Belmont Resident's Avatar
 
Join Date: Apr 2004
Location: Belmont NH but prefer Jackman Maine
Posts: 1,857
Thanks: 491
Thanked 409 Times in 251 Posts
Default Mike Mahoneys plumbing & heating in Alton

Look him up he is listed, he does all of the plumbing for one of the crews I work with. Excellent to work with and resonable rates.
Belmont Resident is offline   Reply With Quote
Old 09-09-2010, 07:00 PM   #4
NoBozo
Senior Member
 
Join Date: Jun 2008
Location: Portsmouth. RI
Posts: 2,231
Thanks: 400
Thanked 460 Times in 308 Posts
Default

Each ZONE of a Baseboard Hot Water system has a Zone Valve. It's in the cellar near the furnace. It's controlled by the thermostat up in the room, or area for that zone. The thermostat is not likely the problem. The zone valve in your case may be "sticky" or reluctant to function. As often as not.. just replacing the "Electric" part of the zone valve....a seperate component ON TOP of the mechanical valve itself fixes the problem

Hire a plumber and the cost goes UP. NB
NoBozo is offline   Reply With Quote
Old 09-09-2010, 07:41 PM   #5
DickR
Senior Member
 
Join Date: Apr 2008
Location: Moultonborough
Posts: 738
Thanks: 4
Thanked 256 Times in 168 Posts
Default

It also might be that there is an air pocket in that loop that hasn't been bled. The circulator produces just enough head to move water through the loop if it is totally filled with water. Checking this costs nothing and ought to be done before spending money for parts or a plumber.

Look at the elbows at the ends of the loop. One of them ought to have a small valve in it. Open it until air bleeds out and there is just a squirt of water. You'll want to have a rag under it to absorb the water, and you may have to use an offset screwdriver to get into the restrictive space. And mind your knuckles on the aluminum fins on the pipe, as they are sharp. This may not work if the run of pipe is not level and the bleed valve is at a low point.

If you can't bleed the air out that way, then you may be able to do it through the water makeup valve on the system. Hook up a hose (an old washing machine hose is nice and short) to the drain valve on that loop and run the end into a bucket. Close the valve going from the circulator to the boiler, open the drain valve, and, if necessary, open the pressure regulator bypass valve. The rush of water into the system will quickly flush out any trapped air.
DickR is offline   Reply With Quote
Sponsored Links
Old 09-10-2010, 09:51 AM   #6
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

If you only have 1 circulator pump then I doubt there is air in just that zone.If you have a pump on each zone which I do then I would look at purging that zone as previously posted.If that does not solve it you might have a broken pump or impeller.Either way it should be an easy fix for a service man.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 09-10-2010, 10:47 AM   #7
Whimsey
Senior Member
 
Whimsey's Avatar
 
Join Date: Aug 2007
Location: Rum Point/West Alton
Posts: 196
Thanks: 261
Thanked 37 Times in 24 Posts
Default Thanks to All for the Helpful Advice

I'll give these a try before calling in a service guy. Thanks a lot.
Whimsey is offline   Reply With Quote
Old 09-10-2010, 03:42 PM   #8
jmen24
Senior Member
 
Join Date: Feb 2009
Posts: 1,139
Thanks: 223
Thanked 319 Times in 181 Posts
Default

Quote:
Originally Posted by NoBozo View Post
Each ZONE of a Baseboard Hot Water system has a Zone Valve. It's in the cellar near the furnace. It's controlled by the thermostat up in the room, or area for that zone. The thermostat is not likely the problem. The zone valve in your case may be "sticky" or reluctant to function. As often as not.. just replacing the "Electric" part of the zone valve....a seperate component ON TOP of the mechanical valve itself fixes the problem

Hire a plumber and the cost goes UP. NB
Zone valves usually stick either open or closed, but you could be correct. They will not product warm, its hot or cold. Some heating systems run independant circulators to each zone for baseboard heat or radiant so zone valves are not always present. Really depends on how far the water needs to be pushed or pulled.

Couple of things to check. (the silly "I should have thought of that stuff" before hiring a plumber)

1. Have you verified that the pipes are not getting hot or are you just not gettting the same kind of heated air from the baseboard unit. If the pipe is HOT, but no heat, check to make sure that carpeting is not ubstructing the flow of air from the bottom of the baseboard.

2. If you have zone valves, here is the test to determine if they are working. Remove the wire from the number one terminal on the head of the zone valve. Once removed, pull the little lever all the way down and turn on a thermostat on another zone. If the zone in question heats up as normal, then the head of the zone valve is bad. (disconnecting the wire from the head ensures that a signal cannot be sent to the zone valve by the thermostat. If a signal is sent to open the valve after it has manually been opened it will damage the head and it will need to be replaced.

3. If you have circulating pump zone control, the zone that is not circulating will make no noise when the thermostat is turned on. The circulating pump will get TERRIFICALLY HOT to the touch. I say it that way, because they will get hot in normal use, but "putting your hand on the stove, hot", when they are siezed.

4. Check to see that a ball valve controlling the zone has not been closed slightly. There should be one valve at the start of the loop and one at the end (located after a sill cock, for draining the line). A slightly closed valve will constrict the flow of water in the loop and reduce the heat output on that zone. It can also cause the loop to get airbound. If this is the case, post back and I can walk you through fixing that issue. An airbound line in a fully open loop and on only one zone, is the cause of another issue that will require a plumber to pressure test the system to find an air leak in a connection.

Those are the quick and easy problems that you can check yourself and are the cause of a single zone failure issue 9/10 times. Good luck.
jmen24 is offline   Reply With Quote
The Following User Says Thank You to jmen24 For This Useful Post:
Whimsey (09-14-2010)
Old 09-10-2010, 06:47 PM   #9
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Default

If it is air bound it is the expansion tank not working properly and removing the air when the system is running.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 09-10-2010, 10:28 PM   #10
RI Swamp Yankee
Senior Member
 
RI Swamp Yankee's Avatar
 
Join Date: Jul 2002
Location: North Kingstown RI
Posts: 688
Thanks: 143
Thanked 83 Times in 55 Posts
Default

DickR and jmen24 have good advice.

I have a system with just one continous loop for the house, one zone. A couple of years back I had the same problem, sort of hot near at the first baseboard near the furnace, lukewarm at the end of the loop. Water temp at furnace was HOT. No air bleed at the high point of the system. I was convinced it was the circulator but I could not find a replacement. I connected a hose to the drain, ran it out the basement window and drained it. I closed the return valve, opened a drain valve just above the return, and opened the water supply valve. This fed water through the furnace, through the loop upstairs and back down to the drain just above the return valve and pushed air out the drain valve. When I heard the water sloshing back down the return line I closed the drain which was located in the retun pipe and near the top of the furnace.

In short, purging and refilling the system may get it working again. Also make sure you bleed air from the "air scoop" if you have one.
__________________
Gene ~ aka "another RI Swamp Yankee"
RI Swamp Yankee is offline   Reply With Quote
Old 09-10-2010, 10:56 PM   #11
Argie's Wife
Senior Member
 
Argie's Wife's Avatar
 
Join Date: Oct 2004
Location: Alton
Posts: 1,908
Blog Entries: 1
Thanks: 533
Thanked 579 Times in 260 Posts
Default

I assume you get your furnace serviced each year, so why not just ask them to troubleshoot your problem?

We had a similar issue and a new zone valve was installed - problem solved. It was a $5 part and took less than 30 min to install... Problem hasn't returned.
Argie's Wife is offline   Reply With Quote
The Following User Says Thank You to Argie's Wife For This Useful Post:
trfour (09-11-2010)
Old 09-13-2010, 07:14 AM   #12
jmen24
Senior Member
 
Join Date: Feb 2009
Posts: 1,139
Thanks: 223
Thanked 319 Times in 181 Posts
Default

Quote:
Originally Posted by Argie's Wife View Post
I assume you get your furnace serviced each year, so why not just ask them to troubleshoot your problem?

We had a similar issue and a new zone valve was installed - problem solved. It was a $5 part and took less than 30 min to install... Problem hasn't returned.
I can assure you that a zone valve was not replaced for $5 in parts. A Taco standard duty zone valve head alone is about $60 and an entire assembly runs about $85, contractor cost. A circulator is in the same price range. http://www.pexsupply.com/Taco-555-05...-570-3708000-p

RLW, the expansion tank is not in the system to remove air. The auto bleeder at the top of the return line above the boiler does that. The expansion tanks sole purpose in the heating loop is to take up the expanded volume of hot water as a direct result of heating it.
jmen24 is offline   Reply With Quote
The Following User Says Thank You to jmen24 For This Useful Post:
RLW (09-15-2010)
Old 09-13-2010, 07:43 AM   #13
Slickcraft
Senior Member
 
Join Date: Mar 2008
Location: Welch Island and West Alton
Posts: 3,240
Thanks: 1,187
Thanked 2,018 Times in 924 Posts
Default

We have one circulator pump and three zone valves. Each fall at least one of the 2nd floor zones is air bound and hot water either will not circulate at all or very slowly.

It is a simple matter to purge each zone on our system so I do it myself. In the beginning I asked the service tech to trouble shoot it during annual service, as AW has suggested. He then showed me how to purge a zone. Even if this is not your current problem, in the future it can be a first action prior to deciding to call for service
Slickcraft is offline   Reply With Quote
Old 10-01-2010, 03:34 PM   #14
Whimsey
Senior Member
 
Whimsey's Avatar
 
Join Date: Aug 2007
Location: Rum Point/West Alton
Posts: 196
Thanks: 261
Thanked 37 Times in 24 Posts
Default Thanks

Thanks to everyone for their input. To round out the story, I couldn't resolve it myself. It turns out one of the circulator pumps had failed. Had Mike Mahoney fix it. Thanks again.
Whimsey is offline   Reply With Quote
Old 10-01-2010, 04:02 PM   #15
tummyman
Senior Member
 
Join Date: Aug 2009
Location: Moultonborough
Posts: 791
Thanks: 236
Thanked 635 Times in 230 Posts
Default Purging System

I had an old plumber show me a trick when purging the system. Use a hose from the boiler and run it into a 5 gallon pail full of water. When you open the purge valve, you will actually see all the air bubbles come out of the system bubbling up in the 5 gallon pail. When the bubbles stop, you are done. Simple but effective.
tummyman is offline   Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 04:16 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.28179 seconds