The Real BigGuy 07-01-2019 07:09 AM

Electrical Question
 
My 240 volt water heater’s connected to an old style pull handle box with 2 screw in fuses, both 30 amp. The connection at the heater is 2 wire with an additional ground.

I rarely work with 240. My question is, do the 2 30 amp fuses effectively make this a 60 amp circuit? It should only be a 30 amp so I want to reduce the fuse size if necessary.


Sent from my iPhone using Winnipesaukee Forum mobile app

jbolty 07-01-2019 07:27 AM

30 on each leg. what you have is fine as long as the wire is at least #10.

swnoel 07-01-2019 10:02 AM

Quote:

Originally Posted by The Real BigGuy (Post 314392)
My 240 volt water heater’s connected to an old style pull handle box with 2 screw in fuses, both 30 amp. The connection at the heater is 2 wire with an additional ground.

I rarely work with 240. My question is, do the 2 30 amp fuses effectively make this a 60 amp circuit? It should only be a 30 amp so I want to reduce the fuse size if necessary.


Sent from my iPhone using Winnipesaukee Forum mobile app

You may have a 60 amp service, but the circuit is 30 amp. No need to reduce anything. As was said by the earlier post, just make sure you have a minimum 10 wire to water heater.

The Real BigGuy 07-01-2019 07:18 PM

Thanks for clearing that up. Forgot about “legs”. The wire size isn’t an issue and It is a 100 amp service. Feel better now.


Sent from my iPhone using Winnipesaukee Forum mobile app

SIKSUKR 07-03-2019 12:06 PM

a 240 30 volt circuit would draw the same as 60 volts of 120 fwiw.

SteveO123 07-03-2019 12:27 PM

Quote:

Originally Posted by SIKSUKR (Post 314527)
a 240 30 volt circuit would draw the same as 60 volts of 120 fwiw.



umm its Amps...

brk-lnt 07-03-2019 12:36 PM

Quote:

Originally Posted by SIKSUKR (Post 314527)
a 240 30 volt circuit would draw the same as 60 volts of 120 fwiw.

In this case, it's "worth" very little. :)
That comment is a tad confusing.

jbolty 07-03-2019 01:51 PM

1 Attachment(s)
…………………. …………..

LIforrelaxin 07-03-2019 02:53 PM

Quote:

Originally Posted by SIKSUKR (Post 314527)
a 240 30 volt circuit would draw the same as 60 volts of 120 fwiw.

Or a different explanation...

240V X 30A = 7200 watts
120V X 60A = 7200 watts

most water heaters consume between 4500 and 5500 watts....

going back the other way with that piece of information you see that if all is good in the world, of your 60 or 30 Amp circuit you are really only using

5500 W / 240V = 22.9 AMPs
5500 W / 120V = 45.8 AMPs

on the lower side we have

4500W / 240V = 18.75 AMPs
4500W / 120V = 37.5 AMPs

so there... now it should be less confussing....

The Real BigGuy 07-03-2019 05:49 PM

Thank you! Ohm’s law[emoji106]


Sent from my iPhone using Winnipesaukee Forum mobile app