Post Furnace Problem ?

Hope I can gets some feedbak on a recent furnace issue, I experienced.

The facts:
Oil fired furnace: Weil-McClean
Beckett Burner
Forced hot water system
Tank located in a shed outside of house-Shed is heated by furnace heated
generated, so never gets cold or freezing
#2 Oil used - treated with 'Hot Shot'
Power-Vent Exhaust - from furnace room to outside

Issue:

This morning I woke up, and house seemed very cold, so I turned up the thermostas, and didn't think anything of it. However, when I went to take a shower, I had 'no' hot water, zip, nada ! Just cold water coming out.

That know, I wne to the furnace shed, and sure enough the furnace had shut down. I have no idea, how long it was in this state, but shutdown, sometime between midnight and 7am.

Just FYI:
Have had many recent parts replaced on furnace and Power-Vent, and basically all tuned-up, by Oil dealer. I'm talking repairs within the last 2 wks. Wondering why the furnace shut down, for no reason?

Now I don't know if this is a factor at all, but yesterday and all night long there were VERY high winds ! Could this somehow be a factor, and maybe the wind caused some back-drafts to the furnace, and shut it down?

I might be reaching on this one, but I have no other explanation?

Anyone have thoughts or ideas about the furnace failure.

Thanks,
BD
bigdog is offline   Reply With Quote
Old 02-20-2011, 05:02 PM   #2
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Power Vents are notorious for locking out burners and it could be the fan prover switch.

The fan prover switch is activated when the power vent take out fan comes on. If the switch is faulty or the tube that goes from the fan to the prover switch is plugged up then the burner will not startup.

Most burner technicians will clean the tube that goes to the switch each time that the burner is tuned up.

Questions:

1. What is the make of your power vent? Tjernlund is the most popular one.
2. Did you press the reset button for your burner and if you did what happened?
Rusty is offline   Reply With Quote
Old 02-20-2011, 05:54 PM   #3
robmac
Senior Member
 
robmac's Avatar
 
Join Date: Jan 2005
Location: Nashua,Meredith
Posts: 951
Thanks: 213
Thanked 106 Times in 81 Posts
Default

Kevin,disconnect power to the unit for 1 minute and turn back on se if it resets. How much fuel in tank?
robmac is offline   Reply With Quote
Old 02-21-2011, 08:03 AM   #4
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Default

Call the oil burner company.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 02-21-2011, 09:06 AM   #5
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue?

Thanks for the feedback, greatly appreciated !

Latest status, furnace started !

I pressed the 'reset' button for about 1-2 seconds, then released, and furnace blower came on for 30-45 seconds. I believe that's what it's suppose to do? However, it shutdown right after this.

Since I was already down on my knees, I figured I just say a prayer !
I then said to myself, I'll give it one more try. I did remember though, the last time the oil dealer performed same furnace reset, he held the 'reset' button in, for about 30 seconds, then released it, so I did same this time.
Wha-la ! Furnace started ! Yippee ! I suspect holding the reset button for the 30 seconds must have been shooting oil into the burner, and maybe first time, didn't have any oil in burner to keep it going? Again, just a big assumption on my part? However, when the furnace did come on, a huge puff of black smoke came out of burner, and I suspect at exhaust vent also.
Long story short, furnace is running and has been for 24hrs without any issues so far?

Rusty,
Just to let you know, the tube that goes from the fan to the prover switch
was cleaned out and the ' prover switch' itself was replaced with new in the last 2 wks. Oil dealer said it was faulty, as a result of the furnace issues 2 wks ago. Again, "Do you think the 'wind' had any factor in furnace shutdown" ?

Robmac,
I did not shutdown the electricity to furnace, before hitting 'reset' switch, will remember that next time. Didn't see your Post about this until after the fact, but it certainly makes sense.

Oil dealer coming to house soon, anyway to deliver more oil (still have 1/2 tank).

Thanks All !

BD
bigdog is offline   Reply With Quote
Sponsored Links
Old 02-21-2011, 09:35 AM   #6
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Power Vents are very complex and have had some nuisance shutdowns when the pressure safety switch mistakes windy conditions for blocked vents.
We have had some windy weather so that could have been your problem.

Power vents are a cheap way to vent the burner exhaust but they sure can cause a lot of problems if not working properly. I know a lot of burner technicians who refuse to work on any burner that doesn’t have a chimney.

Next time this happens shut your furnace down with the safety switch and then turn it back on to see if it will reset itself.

You want to be careful how many times you try to reset the burner because it could buildup fuel in the burner and cause an explosion.
Rusty is offline   Reply With Quote
Old 02-21-2011, 10:37 AM   #7
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue?

Thanks Rusty about the info. you've provided. I've gotton to know so much about oil furnace heating systems this winter b/c of my own issues, I think I'm ready to take the oil-burner technican Certifcation test myself !

Yes, Power Vents are very complex and a pain in the *** !
I think the recent high winds could have tricked the power vent and/or swotch and shutdown the furnace. I don't have any other explanation for the recent furnace behaviour?

My dealer does and happens to know about the funxtions and repairs to Power vents. I would rip out the power vent, and replace with a chimney, if this was practical, but cannot b/c of the current configuration. I would have to run a 25' foot chimney up the side of the house. Being a Condo, would never get the blessings of the Condo Assoc.to do this, besides the location would make this look VERY ugly.

There is a weight adjustment nut, located on vent stack, that balances the ampunt of air which flows through the furnace. If this isn't adjusted properly I suspect it could cause the power vent switch to not work porperly. Just guessing here?

Next time this happens, I will shut your furnace down with the safety switch and then turn it back on to see if it will reset itself.

FYI, I am very careful how many times I reset the burner because I am aware that oil is pushed into the burner each time 'reset' button is pushed and can build-up. Can you say KABOOM ! Learned that lesson a while ago.
I do want to go to heaven, but I don't want to go today !

Thanks,
BD
bigdog is offline   Reply With Quote
Old 02-21-2011, 10:56 AM   #8
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

bigdog,

Glad to hear that you got your burner going.

When you have a power venting system for your exhaust fumes, this is how it works:

1. The thermostat calls for heat and energizes a relay which activates the power venter. After the venter motor has come up to speed, the pressure switch closes. This closes the circuit to the burner and allows the burner to fire.
2. After the heating requirement has been satisfied, the thermostat circuit will open and deactivate the burner.
3. The power venter operates for a period of time after the burner has shut off to purge remaining flue gases.


Any malfunction is these critical steps will make the home owner very unhappy on a cold and windy day or night.
Rusty is offline   Reply With Quote
Old 02-21-2011, 01:34 PM   #9
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

As Rusty just described, powervents are not complicated at all. They are either on or off using a simple motor. They all have a proving switch which tells the control that the power exhaust is working and lets the burner fire. A heavy wind could be a possible problem but not likely unless the prevailing winds that day were directly at your discharge fitting outside the house. Even then they should work against high winds. It sounds more likely that the burner had a faulty start up for some reason and it needed a reset. Multiple resets are not recommended because each time more fuel will be pumped into the combustion chamber and when it does fire a small explosion could occur. I would definitely call the people that serviced your burner and let them know what happened since it sounds like this condition did not exist before it was serviced.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 02-21-2011, 03:19 PM   #10
robmac
Senior Member
 
robmac's Avatar
 
Join Date: Jan 2005
Location: Nashua,Meredith
Posts: 951
Thanks: 213
Thanked 106 Times in 81 Posts
Default

I have seen alot of power vent tubes that have not been installed properly IE the outside pipe. I always make sure if it's a 90% furnace to have it above the intake by at least 12 inches and that I have a 45 fitting on the end with plumbers cloth stuffed in so no rodents or birds can clog it. Always make sure your outside exhaust is free and clear.
robmac is offline   Reply With Quote
Old 02-21-2011, 08:43 PM   #11
jarhead0341
Member
 
Join Date: Oct 2010
Posts: 39
Thanks: 31
Thanked 5 Times in 5 Posts
Default

I wouldn't bank on the wind being your problem with it being power vented usually they work or they don't have seen very few phantom problems like that ..... one other thing to keep in the back of your mind when its time to replace there are now direct vent boilers no chimney no power vent..... I would get your oil co back out
jarhead0341 is offline   Reply With Quote
Old 03-02-2011, 09:04 PM   #12
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue ?

Just to review, Some days it would run fine, then without warning signs, the furnace would go off for no apparent reason ? I was able to restart the system after several reset attempts. However, it shut off sometime early morning.

FYI, had a new burner motor, and burner motor control installed last Spring. Both found to be defective at that time.

Got the oil dealer back out to house to check the furnace system issue.
Anyway, oil dealer indicated I definitely have a power vent 'motor' problem, as the motor heats up and very hot to the touch. Sometimes you can only touch the motor casing for a few seconds because of the heat generated.

Oil dealer Tech, made many adjustments. and checked the 'Igniter' module. This part throws a serious spark into the combustion chamber which ignites the oil which is being pumped in. This checked out fine, as I watched this with my own eyes as he was testing. MAjor spark, no issues there.
He buttoned everything up, and started the furnace this time w/o any issues. He then left. That was in the morning.

By mid afternoon, I noticed the house getting cold again. I went to check the furnace, and sure enough it was out again. Called the oil dealer again, and he came right out to the house. He rechecked everything he checked earlier that morning. Last thing he checked was the Igniter module. This time there was little, almost no spark. That same morning, the spark was like a lightning bolt ! Igniter DOA ! He replaced the Igniter module with new, furnace started right up and has been running fine (crossing my fingers), ever since. Then again, it's only been 24 hrs. I'll be a believer, that the Igniter was the probable cause, if after 2 wks the furnace is still running.

FYI, I bought this property a year ago, and had a 'Home Inspector' evaluate all the systems in the house. He didn't think any issues about the furnace, then again, he didn't perform any tests on it !

Furnace is about 25 yrs old, and had all original parts So that considered things were basically overdue to happen, just because of age. Previous property owner neglected any furnace maint., tuneups, etc for years and never did a thing for upkeep to keep in best operation.

After property purchase I had a complete furnace tune-up, but nothing at the time was indicating any issues with parts failure.

Hopefully, the furnace mystery has been solved, with the replacement of 'Igniter' module, but still have concerns about the longevity of the 'power vent'.

Praying for Spring and warming temperatures!

BD
bigdog is offline   Reply With Quote
Old 03-04-2011, 10:05 AM   #13
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

I wouldn't expect an inspector to find a problem with your furnace with the situation you described. An intermitent problem is just that, hit or miss. I should have thought of your as I just had my tech at my house to clean my oil fired FHW furnace. He looked at the spark coming off my igniter and showed me how it was very marginal. My igter itself was fine but this showed that my transformer was getting near its end. I could keep using it till it totally died but it was going to happen sooner or later and probably when I was gone for the weekend right? I had him change it out. I should have thought of this as being a possible issue for you. Sounds like you found the problem.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 03-05-2011, 01:41 PM   #14
Kamper
Senior Member
 
Kamper's Avatar
 
Join Date: Jul 2005
Location: Thornton's Ferry
Posts: 1,295
Thanks: 67
Thanked 165 Times in 125 Posts
Default

I had a problem with my ignitor a few years back but forgot all about it until you said that was a likely culprit. I could not get my furnace to go on by hitting the 'reset' though. Since it was not freezing weather I had to wait a couple days for the technician which was not a major issue at that time.

The most frustrating part of the affair was the first thing the technician did was hit the reset button and the darned thing worked! Since he was there he said he'd check things out in more detail. He called me down about 15 minutes later and said watch this...

He had the ignitor coil module in his hand and there were two spring contact abut 3-4 inches apart. He laid a screw driver on one and brought it towards the other. When the blade was about 1/4-1/2 inch from the contact a spark jumped between the two. Apparently if the coil had been working correctly it would have spaked about and inch and a half out. The new part filled the hole but apeared to have spacing engineered into it because after 50 years they had been able to design the coil to be a lot smaller.

The next thing to go a couple years later was the blower on the ignition unit. Same thing, smaller part with a plate to fill the space. That's probably going to be your next thing to go so when you have service again ask the tech if he can inspect it closely and maybe check the resistance, or however they test blower motors.

Good luck with your furnace!
Kamper is offline   Reply With Quote
Old 03-05-2011, 08:57 PM   #15
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Problem ?

SIKSUKR
Ignitier spark was marginal but OK, during first test, the Technician performed early in the morning, but when he came back later in the afternoon, after furnace went out again, there was litterally little if any spark, DOA !
Igniter was replaced Monday, today is Sat., and furnace appears to be running OK, at least it hasn't shudown, since new Igniter part was replaced.

You mentioned 'Transformer' ? That was replaced last Fall 2010.
So you're saying a bad Transformer will affect the amount of spark the Igniter module will create?

Kamper
My Burner Technician did that same test you described with Iignitor coil. LaMy tech did same, laying a screw driver across the 2 coil elemnets, to test the spark. Origianl Igniter proed to have no spark. Replacement Igniter spark was at least 1". Seem to do the trick.

As far as blower motor, replaced that previous Jan (2010) ! $$$


Thanks guys for all the valuable info., much appreciaited!

BD
bigdog is offline   Reply With Quote
Old 03-07-2011, 01:00 PM   #16
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

Quote:
Originally Posted by bigdog View Post
SIKSUKR

You mentioned 'Transformer' ? That was replaced last Fall 2010.
So you're saying a bad Transformer will affect the amount of spark the Igniter module will create?

BD
Oh yes. The transformer gives the ignitor, which is basically like a spark plug, the necessary voltage to generate that spark. It puts out somewhere around 10,000 volts.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 05-08-2011, 04:59 PM   #17
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Problem ?

More furnace issues..... Or maybe just the same one?
FYI, this is an oil furnace heating by FHW.

Furnace just has never really never woked smoothly, for any long length of time. By that I mean like 2-3 weeks time. Over the winter, I've spent over $1000 on labor and parts, and I'm probably underestimating...

Since last year, I think I've replaced all the major components on the furnace, including 'powerr venter'. Latest issue was noticed upon recent arrival to house, after a one week absence. Furnace was off, so I pushed the 'reset button' on furnace, and it came on first attempt. Prior to this, thermostats on both floors of house were set around 55 degrees. After furnace came on, I set the thermostats at 60 degrees, and have left there. That was 2 days ago.

Just went to draw hot water and noticed it was 'luke-warm' !
Checked furnace, and it was 'off' ! @$*(@^$_*(@^*$_@*(^$#&*(^$*
Anyway, hit reset and furnace came on again.

I've had two different oil dealers service this furnace in the last year and a half. I've changed oil dealers b/c I didn't like the service I was given for one reason or another. Enough said ! These guys are suppose to be the
so-called experts, that's why they charge you $80-100 per hour.

I've explained the issue with furnace shutting down, to both oil dealers, and they both completely checked thw system, and cannot identify what is causing furnace to shut down at any given time.?

TG is Spingtime, and not threat of freezing can occur, especially when I may be away from property.

Probably going to seek another oil dealer service, maybe a third source will have a better idea, about furnace shutdown for no reason ?

#1 - Has anyone on the Forum experienced furnace issues as I've described?

#2 - Shouldn't I be able to lower my furnace to say 50-55 degree,
without the furnace shutting off? Or is there possibly some type fo 'low-limit' swithch on furnaces, that will shut down system automatically, if it reaches a low temp?

Any help or information is greatly apprecaited !

BD
bigdog is offline   Reply With Quote
Old 05-08-2011, 05:49 PM   #18
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Did your service people check the photo cell to see if it was dirty or not working? This will shut your burner down if not working properly or dirty. It will startup and run for an extended period of time but will shut down if it doesn’t see a flame.
If your burner is running rich it will clog up the photocell eye and shut the burner down. You can tell if your burner is running rich by looking at the nozzle and the cage around the nozzle. If they are black with soot it could cause a problem with the eye.

As you know the way oil burners work is oil is sprayed through a nozzle at high pressure (at least 100 psig) and is ignited by an electric spark from a high voltage transformer.
Once the oil starts burning there is either a photo cell to detect light from the flame or a thermostat in the stack (chimney) that detects heat from the fire and needs to see it within a certain period of time (usually 45) seconds or it will shut the burner off.
If the flame is not established the circuitry on the control properly called the "Primary" will activate an electric heater on a thermal relay that will pop open after the 45 second time period. After this happens you have to reset the control (after it cools) and you have another 45 seconds.
Newer controls may have an electronic system that gives you like 2 tries to get the oil burner started before it gives up then you must follow a procedure to clear the fault.
Rusty is offline   Reply With Quote
The Following 2 Users Say Thank You to Rusty For This Useful Post:
bigdog (05-08-2011), Kamper (05-09-2011)
Old 05-08-2011, 06:28 PM   #19
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue

Thanks Rusty, very informative feedback.

I know I don't have a thermostat in the stack chimney, so where is this "photo cell" located?

FYI, I have a fairly new Honeywell Primary Oil Control (R7184U) 9 months old, and Beckett Ignitor module, less than 3 mos. old. Contacts adjusted at time of installation.

Not sure if Ignitor or control chamber, or stack full os soot? Would think oil dealer(s) would have checked those things at the time parts were replaced
They're the experts right? I'm just the consumer, writing the checks !

Is the 'photo cell' located in or around the furnace chamber, or maybe in the
"Primary Oil Control " housing?

Thanks,
BD
bigdog is offline   Reply With Quote
Old 05-08-2011, 07:14 PM   #20
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,855
Thanks: 459
Thanked 659 Times in 365 Posts
Default

If the reset is tripped, then it is either not lighting or going out some time after it lights. I'd check the photo cell as Rusty suggests, make sure all connections are good (pull on wires that are in connectors (gently), they should not pull out of the connectors). Other problem could be air getting in the oil line, but the system would probably not restart if this were happening. If the photo eye is sooted up then the burner is not set correctly and needs to be adjusted. Obviously you've checked that you have enough oil in the tank.......
ITD is offline   Reply With Quote
Old 05-08-2011, 07:21 PM   #21
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,855
Thanks: 459
Thanked 659 Times in 365 Posts
Default

Manual on your controller.... http://www.forwardthinking.honeywell...ll/69_1459.pdf

Don't blow yourself up...
ITD is offline   Reply With Quote
Old 05-08-2011, 07:36 PM   #22
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Problem ?

Thanks ITD for link on Honeywell Controller.

BTW, the last time I hit reset button, I held in for about 10 seconds then released. After about 15-20 seconds the burner kiked on and a huge blast of black smoke, came out my power venter. I suspect as a reults of an accumulation of oil in the combustion chamber. Next time, I'll just hit the reset button and release immediately ! Can you say KA-BOOM ! Not funny !

FYI, service tech also replace wom type of swithc on the power vent recently. As you know, if the power venter is not working, you'll NEVER start the furnace. It's a built-in safety feature. Darn powere ventors, I hate them, lots of trouble.

Also, which I didn't mention, is the furnace is located in a small outside room
(8x3) attached to the main building, but definitely separate. Have been told that this furnace room space, may not be getting enough air-flow exchange into the area, which could cause a shut-down of furnace. Also I guess a possibility ? Sort of makes ense ?

Will check wires in control module and photo cell next.

Thanks,
BD
bigdog is offline   Reply With Quote
Old 05-08-2011, 08:09 PM   #23
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,855
Thanks: 459
Thanked 659 Times in 365 Posts
Default

From what you are describing I would suspect the ignitor system. The electrodes have to be located properly with the proper gap for the burner to light correctly, sounds like you have replaced most of the other parts although sometimes you get infant mortality.

If it were an issue with the power vent, the burner would not get the chance to light so the reset button would not get the chance to trip.

My guess anyway.

Page 5 of this manual shows the measurements for this particular model burner. It's important that they measure this with a gage or a ruler, a lot of guys just eyeball it......... I wouldn't mess with this unless you know how to open the burner up, but I wouldn't hesitate to look over the guy's shoulder and ask questions.

http://www.beckettcorp.com/protect/t...AF%20R0803.pdf
ITD is offline   Reply With Quote
Old 05-08-2011, 08:41 PM   #24
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue

ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.
I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
bigdog is offline   Reply With Quote
Old 05-09-2011, 09:08 AM   #25
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by bigdog View Post
ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
I have a Carlin burner and it is under the transformer/primary control. When you flip it up you can see the CAD cell and it looks like this:

Rusty is offline   Reply With Quote
Old 05-09-2011, 09:31 AM   #26
VitaBene
Senior Member
 
VitaBene's Avatar
 
Join Date: Jul 2007
Location: Moultonborough
Posts: 3,527
Thanks: 1,561
Thanked 1,599 Times in 820 Posts
Default

Rusty has given you some great info.

Unfortunately, it seems like your technicians are not diagnosing the problem, but instead are throwing parts at it. This is usually a sign of someone who lacks good troubleshooting skills, perhaps you need to try a different company?
VitaBene is offline   Reply With Quote
Old 05-09-2011, 09:41 AM   #27
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Problem ?

Rusty,
Thanks for the great picture of Cad Cell and Ignitor terminals.
Thought it was in this location.

VitaBene,
Taking your advice,to get new service tech provider.
Made that decision after the last fiasco failure !
bigdog is offline   Reply With Quote
Old 05-10-2011, 06:51 AM   #28
tummyman
Senior Member
 
Join Date: Aug 2009
Location: Moultonborough
Posts: 774
Thanks: 231
Thanked 628 Times in 226 Posts
Default Pressure check

One thing that gave me headaches a while back was the pump pressure setting. My burner was set too low, causing flame-outs. The pressure should be around 180PSI I believe. Have the tech check the actual pressure setting vs. the burner spec. A simple adjustment has resolved all my prior issues. I went through techs also changing all the parts out, only to find it was a pressure issue. May be worth a look......
tummyman is offline   Reply With Quote
The Following User Says Thank You to tummyman For This Useful Post:
bigdog (05-10-2011)
Old 05-10-2011, 10:09 AM   #29
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Default

Quote:
Originally Posted by bigdog View Post
ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.
I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
If you had a half a** tech come into your house to service your burner 99.9% of all the suggestions given would have bee checked for proper service. I'm not sure there really is such a person as an EXPERT burner servicemen. Time makes knowledge, but defiantly not and expert.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 05-10-2011, 01:57 PM   #30
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue?

ITW,

Couldn't agree with your comments more.......

Spent a lot of $$$ and getiing half-***** service.

Hopefully, the next "new guys" on site will resolve my issue. That's a big TBD.

BD
bigdog is offline   Reply With Quote
Old 05-11-2011, 08:03 PM   #31
SPT13
Senior Member
 
Join Date: Jan 2009
Location: Weymouth Ma/Gilford when I can!
Posts: 63
Thanks: 112
Thanked 7 Times in 7 Posts
Default

Bigdog,
have you called Weil McLean at all? I had a situation like yours yrs ago and after watching guys change parts and having the same issues I called the manufacturer. I told them the problem, and they recommended a local guy who knew the furnace like the back of his hand. He had me up and running soon with no issues. Good luck!
SPT13 is offline   Reply With Quote
The Following User Says Thank You to SPT13 For This Useful Post:
bigdog (05-11-2011)
Old 05-12-2011, 09:31 AM   #32
SAMIAM
Senior Member
 
Join Date: Apr 2004
Location: Moultonborough
Posts: 2,834
Thanks: 326
Thanked 1,625 Times in 561 Posts
Default

Lesson to be learned is...shop carefully for a service company.Get recommendations from friends and neighbors.Makes me crazy when I call for service and they send some lunkhead that doesn't know what he's doing.You pay a service charge,travel charge,gas surcharge,labor rates as high as $85 and outrageous mark up on parts only to find it's still not working.So you call them back and they try something else that fixes the problem ...or maybe not.You just keep paying for someone to experiment until they stumble on the solution.
Even had a refigeration guy charge me for 2 techs at $85/hr only to find out the guy had his 10 year old son with him running for tools.
We have great luck with Lakeside Plumbing for heating and plumbing issues.The usually get it right the first time.When you call their office you get a real person and the gals that answer the phone can diagnose as good as any of the techs.They show up when promised and have emergency service.
SAMIAM is offline   Reply With Quote
The Following 2 Users Say Thank You to SAMIAM For This Useful Post:
CateP (05-12-2011), VitaBene (05-12-2011)
Old 05-19-2011, 07:36 AM   #33
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
Default Furnace Issue ?

More feedback to Forum regarding furnace problem.....

Just checked 'photo-cell', and it appears to be brand new. The Beckett Igniter module was recently replaced, and it looks like the photo cell, came included new and packaged with that module. I did clean the photo cell eye, and checked all wires, and all appears to be fine.

Furnace will start, and run for a while, but at various intervals will shut down w/o reason?

Primary Control goes into a 'restricted/lock-out sttate, but seems I can always reset w/o issues. When I do reset and furnaces starts, I get a huge plume of black smoke, ejected out my power-venter. I suspect this as a result of built-up oil, inthe burner chamber which did not origianilly ignite?
Guessing?

Next step will be to call Weil McClain to get some input from them. Maybe mu issues, is something, common to this brand of furnace, that requires specific settings? Also have called another P & H contractor recommended by a Forum member, and will be coming to house to review the issue.

Thanks,
Bigdog
bigdog is offline   Reply With Quote
Old 05-19-2011, 01:37 PM   #34
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,855
Thanks: 459
Thanked 659 Times in 365 Posts
Default

If you checked the cad cell, you were a couple of steps away from removing the nozzle/electrode assy. If you are comfortable, you can give this a try, I'm thinking the electrodes are bad or more likely from your prior description of how it was installed last time, just not installed correctly. Good luck, don't blow yourself up.
ITD is offline   Reply With Quote
Old 05-23-2011, 07:58 PM   #35
sparky63
Junior Member
 
Join Date: May 2004
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by bigdog View Post
More feedback to Forum regarding furnace problem.....

Just checked 'photo-cell', and it appears to be brand new. The Beckett Igniter module was recently replaced, and it looks like the photo cell, came included new and packaged with that module. I did clean the photo cell eye, and checked all wires, and all appears to be fine.

Furnace will start, and run for a while, but at various intervals will shut down w/o reason?

Primary Control goes into a 'restricted/lock-out sttate, but seems I can always reset w/o issues. When I do reset and furnaces starts, I get a huge plume of black smoke, ejected out my power-venter. I suspect this as a result of built-up oil, inthe burner chamber which did not origianilly ignite?
Guessing?

Next step will be to call Weil McClain to get some input from them. Maybe mu issues, is something, common to this brand of furnace, that requires specific settings? Also have called another P & H contractor recommended by a Forum member, and will be coming to house to review the issue.

Thanks,
Bigdog
Hi Bigdog
Im a tech for a large oil company . from what you are discribing everything is working right up to the point of ingition ( I get a huge plume of black smoke, ejected out my power-venter.) you need 3 things to make combustion you also need them in the right amounts to much air will lean out the mixture to the point of not firing. to little spark will also not let it fire
sparky63 is offline   Reply With Quote
Old 05-23-2011, 08:02 PM   #36
sparky63
Junior Member
 
Join Date: May 2004
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default

bigdog pm me mby i can help i'm not much for typing
sparky63 is offline   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 09:57 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.

This page was generated in 0.34076 seconds